Out interest how would you calculate R1+R2 for a star delta motor . The contactors are in a control panel .
 
Last edited by a moderator:
Same as you would on any R1+R2 circuit, obviously Motor Contactor & Motor connections.Ideally before you connect any cabling.
Being connected in CP this should be ok with normal tests required @ the Panel😎
 
Measure the length of the cable, establish the resistance per metre and calculate from there.
 
  • Funny
Reactions: mainline
Measure the length of the cable, establish the resistance per metre and calculate from there.
I can just imagine the OP trying to measure the cable length whilst it runs through roof voids, cable tray etc and then end up with having to disconnect, link out and measure it properly.
 
  • Like
Reactions: cliffed
I can just imagine the OP trying to measure the cable length whilst it runs through roof voids, cable tray etc and then end up with having to disconnect, link out and measure it properly.

You are assuming that this is an existing installation.

I am assuming it is a planned installation, I've based this on the design stage being the only time I would normally calculate these values.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Stoke on Trent
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
Out of interest how would you calculate R1+R2 on cables running from a control panel to a Star delta motor?
Prefix
UK 
Forum
UK Electrical Forum
Start date
Last reply date
Replies
4

Thread Tags

Advert

Thread statistics

Created
Neil B,
Last reply from
Brother Blue,
Replies
4
Views
284

Advert