Hi,

Been asked to look at installing an electric hob and electric oven to existing circuit in a rental property this evening. Details are a bit sketchy at the moment, but I do know:

The CU was recently replaced with a dual RCD unit. EIC and Part P certs are available.
The existing circuit is protected by a 32A MCB, and run in 6mm T+E. Length is < 10m.
There is an isolator switch above the worktops, this then goes to a flex outlet unit.
At the moment there is nothing coming from the flex outlet unit.
As far as I know, there is no FCU, although apparently the EIC states that the circuit serves 2 points.

I don't know what the ratings of the appliances are yet, but for now I'm assuming that the hob will be ~6200W, and the oven ~2400W. So, with diversity, they should both be OK on a 32A supply. Obviously I'll check the ratings when I see the appliances. I should also be able to see the manufacturer's instructions this evening.

My concerns are:
1) Will the flex outlet unit be suitable for two cables leaving it?
2) Will the cable from the outlet unit to the oven require fusing down to 13A?

If I do need to fuse down, I guess I can either use an FCU, or a socket and plug?
 
i would be inclind to wire the hob direct and FCU the oven
 
Hi,

My concerns are:
1) Will the flex outlet unit be suitable for two cables leaving it?

The only cooker outlets i have handled have been designed for a single flex/cable, and would be too cramped to get two in. I have searched for a double one (as might want one myself) but couldn't find one. However, i do have a recollection of seeing a double version, possibly posted on this forum (?)
Anyone come across a double outlet or have a link to one?
Or even an isolator that has space to supply two outlets?
 
I was afraid you'd say that. I was hoping I could just wire in, without modifying the fixed installation, as that makes it notifiable.
 
can you apply diverrsity if appliance allows all cylinders d fly at once.. cooking for 10 ppl
 
can you apply diverrsity if appliance allows all cylinders d fly at once.. cooking for 10 ppl
:confused: but yes. Once ovens/hobs have been on a little while they are not using max power even if they are set on max temp.
 
hmmmm , pushrod you amaze me how little i know, can you define a sum for this. how would you work it out??? sorry if your busy
 
The first 10A of the rated current plus 30% of the remainder of the rated current plus 5A if a socket outlet is incorporated in the control unit. (from memory) - check OSG which is not beside me at the moment!
 
temperature set switch ie thermostat constantly switching it on and off. Once it reaches the set temp it will spend a lot of the time being "off" , particularly a well insulated oven. The elements only come back on to raise the temp a little when it has cooled (to the set temp) and then switch off again. :)
 
if you remember the pg number i will be impressed, aand i will get my book and hve look
 
so if i have 30 amp cooker i can clip direct 1.5mm as can take more than 16 amp, which is you first 10amp + 30%
 
Ha ha - I'm at home having my lunch, copied that from old brown osg (red one at work -so may have changed) My memory is not that good :)
 
so if i have 30 amp cooker i can clip direct 1.5mm as can take more than 16 amp, which is you first 10amp + 30%

Yes, but only if you put it on a 16A breaker.

My original question wasn't really about diversity. It's about having a 10A (without diversity) oven connected to a 32A 6mm supply. Does it need to be fused down, or is overload of the cable unlikely enough that this isn't required?
 
Last edited by a moderator:
Why don't you connect with 10mm as well - then no worries!
 
Hang on - I'm getting confused here. Just noticed your original post mentions 6mm T&E now you're talking about 10mm?
 
Yes, but only if you put it on a 16A breaker.

And it would have to be a very short run as you would very quickly run into volt drop problems. In reality no one would do it.

My original question wasn't really about diversity. It's about having a 10A (without diversity) oven connected to a 32A 10mm supply. Does it need to be fused down, or is overload of the cable unlikely enough that this isn't required?


Thought you said 6mm? in OP . The breaker is there to protect cable. If you go down at the outlet to something that can't handle 32A then you would need to put a fuse in.
 
any cooker ive connected 1 cable, squeeze them in 1 isolater lol ive lot to learn
 
rryles , sure your not a window cleaner;)
 
no, it was personal joke, dont mind me,
 
The breaker is there to protect cable. If you go down at the outlet to something that can't handle 32A then you would need to put a fuse in.

I thought as much, but hoped otherwise. Maybe I'll be lucky and the oven will come with 4mm flex.

Just to check - I can fuse down using an FCU, or a BS1363 plug and socket?

I presume connecting a 2.4KW oven into the kitchen ring would be frowned upon? I seem to recall anything over 2KW should be dedicated circuit. Just want to be clear on all the options.
 
but why if it is designed already to take nearly 3kw
 
I thought as much, but hoped otherwise. Maybe I'll be lucky and the oven will come with 4mm flex.

Just to check - I can fuse down using an FCU, or a BS1363 plug and socket?

I presume connecting a 2.4KW oven into the kitchen ring would be frowned upon? I seem to recall anything over 2KW should be dedicated circuit. Just want to be clear on all the options.

Agree :)
 
I thought as much, but hoped otherwise. Maybe I'll be lucky and the oven will come with 4mm flex.

Just to check - I can fuse down using an FCU, or a BS1363 plug and socket?

I presume connecting a 2.4KW oven into the kitchen ring would be frowned upon? I seem to recall anything over 2KW should be dedicated circuit. Just want to be clear on all the options.

yes this is what they say. but if you bought a tumble dryer you wouldnt do this, you would just plug it in. however a fixed applience should have an accesable means of isolation
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
Oven and Hob Cable over current protection
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
26

Advert

Thread statistics

Created
rryles,
Last reply from
nick611,
Replies
26
Views
5,571

Advert