Re: Plastic Water main with coper throughout.

Just put one in cover your back as water still conducts and you dont know how far the plastic main goes I'm obviously using my immagination here but at least it has a MPC anyway the water my be connected to a gas combi or something. I would not dwell on this issue just put one in

No you shouldn't "just bond" without testing and a proper assessment, you may introduce a hazard where none previously existed.
 
  • Like
Reactions: 4 people
Re: Plastic Water main with coper throughout.

If the results of your test on the water main have been affected by the main bond to the gas then you have not carried out the test correctly.

Isolate the installation, then disconnect the earthing conductor from the MET (or remove test link). You then test between the incoming earth and the suspected extraneous part.

I'm not surprised you have been accused of trying to get work by unscrupulous means, a plastic water main which feeds surface clipped installation pipework is unlikely to be extraneous.

That was really good advice until the last paragraph. No need for that and ruined the thread IMO.
 
  • Like
Reactions: 1 person
Re: Plastic Water main with coper throughout.

Water alone is non-conductive, impure water such as that which is supplied by the public water mains has limited conductivity.
As far as I know the volume of water in a 600mm length of 22mm plastic pipe has sufficient resistance as to be considered an insulator at 250V

Finally somebody has grasped it!! :)
 
Re: Plastic Water main with coper throughout.

Was called to a job yesterday where a company had completed an EICR on a house fed via a plastic water main with internal plumbing done completely in copper. They had put a c2 observation code for a lack of main protective bonding to the water. The customer had shown me the EIC cert she had been given by the original company who had completed a rewire on her property.
Disconnecting the earthing conductor at the intake position and completing an IR test to the internal stopcock on the water gave me a reading of 0 megohms. To me this has indicated that somewhere within this installation the copper pipework is earthy and deemed extraneous and does warrant a main bond. I did think this could be gaining a reading through the boiler gas connection (which is bonded) I am leaning on the side of advising the client to get the original contractor back to sort this. Opinions on this before doing so would be appreciated.

Why are you carrying out an IR test when you should be measuring the continuity or otherwise of the various components in the system? Surely IR testing serves one purpose only; a proof test of the insulation in a circuit?
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Plastic Water main with copper throughout.
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
45

Advert

Thread statistics

Created
rattlehead85,
Last reply from
GB.Kayak,
Replies
45
Views
6,725

Advert