Re: Plastic Water main with coper throughout.

Just put one in cover your back as water still conducts and you dont know how far the plastic main goes I'm obviously using my immagination here but at least it has a MPC anyway the water my be connected to a gas combi or something. I would not dwell on this issue just put one in

No you shouldn't "just bond" without testing and a proper assessment, you may introduce a hazard where none previously existed.
 
Re: Plastic Water main with coper throughout.

If the results of your test on the water main have been affected by the main bond to the gas then you have not carried out the test correctly.

Isolate the installation, then disconnect the earthing conductor from the MET (or remove test link). You then test between the incoming earth and the suspected extraneous part.

I'm not surprised you have been accused of trying to get work by unscrupulous means, a plastic water main which feeds surface clipped installation pipework is unlikely to be extraneous.

That was really good advice until the last paragraph. No need for that and ruined the thread IMO.
 
Re: Plastic Water main with coper throughout.

Water alone is non-conductive, impure water such as that which is supplied by the public water mains has limited conductivity.
As far as I know the volume of water in a 600mm length of 22mm plastic pipe has sufficient resistance as to be considered an insulator at 250V

Finally somebody has grasped it!! :)
 
Re: Plastic Water main with coper throughout.

Was called to a job yesterday where a company had completed an EICR on a house fed via a plastic water main with internal plumbing done completely in copper. They had put a c2 observation code for a lack of main protective bonding to the water. The customer had shown me the EIC cert she had been given by the original company who had completed a rewire on her property.
Disconnecting the earthing conductor at the intake position and completing an IR test to the internal stopcock on the water gave me a reading of 0 megohms. To me this has indicated that somewhere within this installation the copper pipework is earthy and deemed extraneous and does warrant a main bond. I did think this could be gaining a reading through the boiler gas connection (which is bonded) I am leaning on the side of advising the client to get the original contractor back to sort this. Opinions on this before doing so would be appreciated.

Why are you carrying out an IR test when you should be measuring the continuity or otherwise of the various components in the system? Surely IR testing serves one purpose only; a proof test of the insulation in a circuit?
 

Reply to Plastic Water main with copper throughout. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Not sure on this one. Mains water is coming up from the ground in lead pipe in bathroom. 2 inches of copper pipe before the stop tap. All...
Replies
4
Views
1K
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
I had a call to a new customer who was experiencing what sounded like nuisance tripping on a kitchen ring. Some background first. It's an MK LN...
Replies
4
Views
739
Just want to know everyone’s approach to testing bonding within houses. I do a lot of EICRs, and I would say more times than not I can never get...
Replies
5
Views
1K
Good afternoon one and all. I, like many non-electricians are having issues regarding the need to have domestic water pipes (plastic entry to the...
Replies
4
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock