why would you code anything? The readings in your example above are way above what is ok

I would say they are not ok for a test applied between incoming and outgoing terminals of an MCB in the open position, the reading should be far higher and it is a sign that the MCB has become damaged, most likely through moisture ingress in this situation.
 
I tested all at 250v getting about 1M with n-l connected in mcb switched off and when tested at 500v I got about 0.05 yet when connected in a terminal block out of mcb I was getting 30M plus
As others have said, perhaps the mcb's have become faulty. Don't understand why your using the mcb's as a connector to do your IR tests, or are you just curious now?
 
Try continuing the IR test across the MCB and see if the reading slowly rises, if so then this is a possible sign of dampness that is being cleared by the testing. If the reading is stable then this would be more likely an MCB fault, however that would be odd for all three if it is not moisture.
I assume there are no signs of overheating of the local busbar?

Though of course if there is a connection through the MCB then it may be picking up the RCD, that could give a low reading.
 
If you are concerned,remove the MCB altogether,and test independently. Then test a known good one,or a new item,and compare...

It has been mentioned that the values are acceptable,but being mindful of the short distance you you are testing across,the likely cause of these readings,and the certainty of a customers digit being applied to it...

If it is on your mind,and the length of this thread ,suggests that,i recommend attending to both the cause,and effect of the issue....

Which may be as simple as a £3 MCB,and an umbrella....
 

Reply to Poor ir on when connected to mcb in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

So was on a call out today and cooker circuit kept tripping the RCD. Disconnected at the board and at the cooker switch and IR’d the cable and...
Replies
9
Views
403
Hi all, Been browsing these forums for a while, always great to learn a new way to skin the same cat. Anyway, cut a long story short, was an...
Replies
11
Views
689
In my line of work it's very rare that I ever have to change a DB. I'm largely in maintenance; occasionally have to add new circuits etc. so in...
Replies
3
Views
649
Hi, looking for some ideas on this. I went to an address on Tuesday following a storm where property has been struck by lightning. When the...
Replies
3
Views
741
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock