Discuss Poor ir on when connected to mcb in the UK Electrical Forum area at ElectriciansForums.net
J
joehat
As above says, when testing ir on three circuits I put each circuits neutral into the line into the mcb and tested from mcb terminal to earth, each result below 1M, I then tried connecting the line and neutral in a terminal block , and the results shot up?????
This consumer unit is in a cold outdoor cupboard as per pics I will post, it did the same on all 3 mcbs on the right hand side, all mcbs where switched down in case anyone asks.
My thoughts where dampness or something wrong with mcbs?
Remove MCB, IR test across it. If low, try blow-drying it and see if the result improves. If so, is cupboard suitable location for CU?
When I tested with the method of l-n in the mcb to Earth 250v was hovering just u under 1M and at 500v was about 0.05 and when disconnected from mcb and used block to connect it shot up to about 30M each circuit was similar in results on the the last 3 mcbs to the right of the pic
In terms of dampness, there are quite a few CU's installed in garages and isolators in meter boxes, without issue. But I guess if the ventilation is poor, condensation can form. I've seen a CU in an integral garage, with corroded neutral/earth bars.
So the question is I guess, this can happen inside an mcb
I'm just wondering, depending on how you carried out your test, if using 500v and conditions inside MCB/RCD were damp, you could get reading through devices, even if they were turned off?
I tested all at 250v getting about 1M with n-l connected in mcb switched off and when tested at 500v I got about 0.05 yet when connected in a terminal block out of mcb I was getting 30M plus
Teste across one of the mcbs at 250v and then 500v and at 250v it came up at 81M and at 500v it came up at about 62M
Thoughts?
Should this be above what the tester can read?
If so would this be the damp getting in and would you cod this c2 or c3 in an EICR?
Thoughts?
why would you code anything? The readings in your example above are way above what is ok
I would say they are not ok for a test applied between incoming and outgoing terminals of an MCB in the open position, the reading should be far higher and it is a sign that the MCB has become damaged, most likely through moisture ingress in this situation.
As others have said, perhaps the mcb's have become faulty. Don't understand why your using the mcb's as a connector to do your IR tests, or are you just curious now?
Try continuing the IR test across the MCB and see if the reading slowly rises, if so then this is a possible sign of dampness that is being cleared by the testing. If the reading is stable then this would be more likely an MCB fault, however that would be odd for all three if it is not moisture.
I assume there are no signs of overheating of the local busbar?
Though of course if there is a connection through the MCB then it may be picking up the RCD, that could give a low reading.
If you are concerned,remove the MCB altogether,and test independently. Then test a known good one,or a new item,and compare...
It has been mentioned that the values are acceptable,but being mindful of the short distance you you are testing across,the likely cause of these readings,and the certainty of a customers digit being applied to it...
If it is on your mind,and the length of this thread ,suggests that,i recommend attending to both the cause,and effect of the issue....
Which may be as simple as a £3 MCB,and an umbrella....
Reply to Poor ir on when connected to mcb in the UK Electrical Forum area at ElectriciansForums.net
So was on a call out today and cooker circuit kept tripping the RCD. Disconnected at the board and at the cooker switch and IR’d the cable and...
Does a SPD need a dedicated way? I need an extra way in this unit for a 3 phase car charger As you can see its a small unit with no extra...
Hi all, Been browsing these forums for a while, always great to learn a new way to skin the same cat. Anyway, cut a long story short, was an...
In my line of work it's very rare that I ever have to change a DB. I'm largely in maintenance; occasionally have to add new circuits etc. so in...
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
