What module, etc, was that?Smart real time data on earth leakage current etc is absolutely available right now as I'm have recently installed such devices but in a domestic setting they are a huge cost if going one per circuit etc, as will wiring radial per room which really isn't necessary imo
Of course its not nessecary. Neither are RCBOs, or AFDDs. RCDs are fine (at the moment, until the regs madate otherwise). But like RCBOs, Radials give you more granularity of control over your power, and make isolating faults a lot easier and mean you can have lower rated breakers in the CU which is safer. Yes it costs more, but its a one-off cost for an ongoing benefit.Smart real time data on earth leakage current etc is absolutley available right now as I'm have recently installed such devices but in a domestic setting they are a huge cost if going one per circuit etc, as will wiring radial per room which really isn't nessecary imo
It is more complicated than that.Ring mains are primarily a legacy configuration from cabling resource limitations of post-war britain. Most eu countries, where those limitations never happened, have radials everywhere instead because they just make more sense.
But like RCBOs, Radials give you more granularity of control over your power, and make isolating faults a lot easier
and mean you can have lower rated breakers in the CU which is safer.
Fault finding is just one reasoning. Say, for example, we want to re-decorate a room. Its easier to isolate just that room, then we can pull the sockets, and switches off the wall and have at it without worry, than either isolating the whole floor, or not turning the power off at all, and just "being careful".Breaking an installation down to help isolate faults suggests an assumption or acceptance that the installation will be susceptible to faults and faults will happen. A better attitude would be to have a good quality installation which is inherently far less likely to suffer a fault.
Depends on what you are protecting against. A ring circuit offers less protection against overcurrent because they have to (by design) have a higher rated breaker. The much lower breaker on a radial means that in a worst case scenario (assuming a short in the socket, or some other over current situation that bypasses the local fuse in the plug) the radial would trip quicker than a ring main would.A good quality installation is safer.
This is not true.A ring circuit offers less protection against overcurrent because they have to (by design) have a higher rated breaker. The much lower breaker on a radial means that in a worst case scenario (assuming a short in the socket, or some other over current situation that bypasses the local fuse in the plug) the radial would trip quicker than a ring main would.
Ok I mis-spoke, saying a ring will trip "quicker" was perhaps poor wording. Obviously the breakers will all break at similar speeds.This is not true.
If correctly designed both situations (RFC or radial) will have sufficiently low fault impedance Zs such that the breaker hits the "instant" magnetic trip point and then it will disconnect in typically 10ms or less. The disconnection speed once in the magnetic trip fault zone (rather than thermal overload trip) is not very sensitive to the degree of over-current.
In all cases for a typical UK home on TN supply the design has to disconnect in under 0.4s under hard fault conditions and in the case of MCB (and related RCBO) that always means hitting the magnetic trip point. There is some difference if fault let-through energy between MCB ratings (see below) but surprisingly small, but again the basic principle of electrical design is the cable size has been selected to meet both the operational current and the worst-case fault condition's heating effects.
As @davesparks has already said the key is to have it correctly designed, installed and tested so it is known that everything is meeting the regulations and nothing has a loose / high-resistance connection or dodgy insulation. Oddly enough this is an aspect where the RFC is better as the figure-of-eight test is very sensitive to even small excess resistance since every socket should be identical during the test so spotting a bad joint or socket with a dodgy switch, etc, is easier.
If you want multiple circuits to allow rooms to be isolated individually, etc, then radial make more sense than the RFC which is better suited to a whole floor, etc, that naturally forms some sort of a loop, but to characterise the radial as safer is completely wrong.
View attachment 104770
It could be possible. I hadnt considered that, but it would mean raising it up higher, meaning my partner couldnt access it in my absense.What is on the other side of the wall? Possible to move the CU into another room, so it isn’t in view as you come into house?
You can make the CU as pretty as you like, but you might still see a great ugly distributors head, fuse, meter and tails.
What about a well made cabinet around it all?
Ok I mis-spoke, saying a ring will trip "quicker" was perhaps poor wording. Obviously the breakers will all break at similar speeds.
I meant that with an increasing current situation, a smaller breaker will trip at a lower current threshold, i.e. "sooner".
So the plugs are rated at 13a, if you plug in a device that (for whatever reason) doesnt break the fuse at 13a and pulls say 25a, a 16a or 20a radial will trip, but a 32a RFC wont. It will keep feeding the full 25a to a 13a socket (potentially overheating it and causing a fire).
In this, admittedly very unlikely, scenario a radial is "safer" than a ring because the design implies a lower rating of breaker and that gives less headroom for unexpectedly high loads.
Your second option is not really permitted by BS7671 in residential installations.You may find a CU that looks pretty smart but finding an electrician to compliment it is altogether another matter and remember electricians run businesses so their profit motive comes first, not you. In the UK the profit motive obliges the electrician to recommend a CU filled with RCBO for every circuit courtesy of 17th Edition Regs, its a win for both electrician and customer but is very expensive. There will be little or no nuisance tripping and the electrician does not need to go to the expense of buying an earth leakage instrument such as a Megger DCM 305E.
When the 18th Edition Regs came along two options presented themselves: the first carried across from 17th Edition in that the board must be entirely filled with RCBO. The second option allowed an RCD to protect a group of MCB just as long as the total leakage current measured down stream was less than 9mA. This allows for a split neutral board to be installed albeit with a risk of nuisance RCD tripping. There is however a third option which is a hybrid combination of the first two.
The CU is split into three parts each with separate neutral bars. The first is to leave spare module slots after the main breaker to accommodate RCBO. The second is for an RCD to monitor a group of MCB power circuits and the third an MCB to monitor another group of MCB for lighting. Have installed or as a prelude to install an audit of leakage currents is undertaken. Circuits like ring mains that feature higher leakage currents use RCBO as do any PV inverters and so on. The cost to the customer of such a CU should be around the £350 mark as opposed to between £700-£950 for a 17th Edition full RCBO board.
Youtube's eFIXX electrician explains the pros and cons of this in his Earth Leakage Currents video.
Your interpretation of BS7671 stands as personal opinion. In the best interests of the OP please provide members with evidence to support your view so that it may undergo peer reviewYour second option is not really permitted by BS7671 in residential installations.
Attitude?@Joules that is exactly what I will do when I get home. You are new to the forum so I will let your attitude pass.
I missed this post on the first pass. What make/model is that ?You could fit one of these, adapted for single phase usage. Plenty of room for 'smart accessories)