Jake1579

i understand what pfc is - the maximum current that flows under fault conditions until protective device is operated.... and i know the difference between the 2 types
prospective earth fault current
prospective short circuit fault current

My question is what (path) would prospective short circuit fault current follow under fault conditions because i know with pefc its going to follow the earth fault loop path ZS so its going to have a low zs value so it trips quick. But what about if there was short on l and n i know if there was the breaker or what ever it would trip but i dont get how i know it will have a low resistance so it does trip quick but what path does it take if it is the earth fault loop path i imagine it will have a low zs but theres no earth involved if its on l and n is there??
 
The PSC fault current path varies depending on the supply arrangement ie TNCS, TNS etc.
 
Prospective short circuit current is the current which will flow through a short circuit of negligable impedance at the incoming supply terminals.

What exactly are you trying to ask here ?
 
say theres a short on live and neutral and you have that fault current flowing through it does that fault current on a short circuit between l and n just go into the protective device and detects that fault current and it just disconnects ??
 
say theres a short on live and neutral and you have that fault current flowing through it does that fault current on a short circuit between l and n just go into the protective device and detects that fault current and it just disconnects ??

The fault current will flow through every protective device upstream of it. One of these devices will clear the fault.
 
Hi dude,if you get out the generic fault path diagrams,which simplify the path from generation to fault,you can imagine,or draw your fault,L to N,and see the path of that fault current,and the protective devices it flows through.

There are some excellent drawings on some of the help threads regarding 2391,2394/5.

There is no shame in a picture,i have used these to learn,to teach,and to explain. Even drawing out suppositions i may have,regarding problems,can confirm things,when expensive components are going to be ordered.

...The Bayeau tapestry isn't on a memory stick......get yer pencil out! :icon12:
 

Reply to prospective fault current in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Confused as to what the earth fault loop is. I'm aware it's the path that fault current takes (Line-Earth) but how many times does fault current...
Replies
7
Views
1K
Anyone know of an RCBO manufacturer, apart from Chint,that includes an indicator in the RCBO to indicate if the trip is a earth fault or an overload.
Replies
2
Views
702
So was on a call out today and cooker circuit kept tripping the RCD. Disconnected at the board and at the cooker switch and IR’d the cable and...
Replies
9
Views
381
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
462
I’m probably going to look stupid here, but it will be worth it if I get the answer 😆, as I can’t fathom it out. I’ve never really thought of it...
Replies
22
Views
713

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock