So no insulation resistance test was carried out whilst operating the switches on the two way circuit, therefore there could easily have been an IR fault that was missed.
The cable is in metal conduit, is the conduit earthed?
If the conduit was not earthed then the fault is unlikely to be a fault to the conduit.
If the conduit is earthed then this would be a likely scenario, the cable has been abraded by the conduit and has now been moved clear of the connection with conduit and so works, but still exhibits risk.

The more likely situation is as Trev says when an accessory screw or retaining bolt is tightened up the core of a conductor is trapped by it and touches the earthed screw, once the cable has been "adjusted|" the core is no longer in contact with the screw and so works fine.

The less likely scenario is if the cables in a switch box are messy and tight then cables can cross over and if a damaged L or N or a CPC that is unsleeeved or poorly sleeved come into contact then this could trip the RCD.

As an RCD trip is because of a fault to earth and not a short circuit the above a re the most likely ideas for what is happening (assuming the circuits are wired correctly, there is no borrowed neutral and so forth).
Full testing whilst there was a fault would have found this situation, which is why we test!
 
Thanks a lot Richard I do find your posts god ones, and I agree mate we should of done a insulation resistance test and I know that's what I would of done. To be fair I did suggest it but u can't be to pushy when your the mate.
 
OP, keep your posts coming. it's getting more like a loony bin daily in here.
 
Apologies if it annoys you that's not my aim but I'll keep them coming as and when something pops up that i'm not to sure about. I did ask to go on the trainee forums but according to Paul I'm to advanced for that ...
 
Apologies if it annoys you that's not my aim but I'll keep them coming as and when something pops up that i'm not to sure about. I did ask to go on the trainee forums but according to Paul I'm to advanced for that ...

it don't annoy me, mate. just winding you up. :willy_nilly:
 
glad to see you're on the road to recovery, geordie. keep lifting them weights ( and TB . that'll get you fit).
 
glad to see you're on the road to recovery, geordie. keep lifting them weights ( and TB . that'll get you fit).

Well all of my cars have been kept off the road while all this has been going on but today I felt optimistic enough to book one of the MR2 s ( that one over there <--------- ) in for repairs & MOT on Friday then get the top opened up and have a blast around the countryside.
 
Well all of my cars have been kept off the road while all this has been going on but today I felt optimistic enough to book one of the MR2 s ( that one over there <--------- ) in for repairs & MOT on Friday then get the top opened up and have a blast around the countryside.

So where are you taking me Geordie? :auto: :smilewinkgrin:
 

Reply to Pulling the cable sorted the problem in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

R
Hi. Can somebody please advice what to do next or should I do anything next or just leave that cable as it is? Just bought the house and found a...
Replies
9
Views
435
Resident
R
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
377
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
854
I got a TEXT message (i dont know them and i cant find out who they are from the phone number) "Hi speaking from Indeed Are you available to give...
Replies
15
Views
921
Can i just check something. If a rat decides to chew a cable will it trip the MCB or RCD ? I ask because I had one house recently that had a...
Replies
10
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top