Hi

I am still training and have a question regarding Insulation resistance test.

My question is when doing the test between live and earth at the consumer unit, what happens to the circuit breakers? On or OFF?

Many thanks.
 
Hi

I am still training and have a question regarding Insulation resistance test.

My question is when doing the test between live and earth at the consumer unit, what happens to the circuit breakers? On or OFF?

Many thanks.

still training ?
youve been a member for 4 years lol.
 
Your question has been answered, but if you are serious about a career in this industry, then by all means keep asking, but you need to invest in your future as well. Get on Amazon, and buy yourself the IET Guidance note 3. This is the testing bible, and covers in depth with explanation and illustration all you will ever need to know, and all for the price of 3 or 4 ****mags.

Cheers...........Howard
 
The best way of doing the test is to disconnect L and E from the CU!

The cpc has to be connected to the means of earthing for the test. Also if conducting the test on a circuit by circuit basis then you must consider the effect of the resistances in parallel.
 

Reply to Question regarding Insulation resistance test. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Replies
9
Views
649
Hi. The question is..... can saturated ground affect earth resistivity testing equipment? Some days there's an unacceptable earth reading, another...
Replies
9
Views
501
Hello everyone, Hope you're all well. I'm carrying out an overall/global insulation resistance test on a newly wired 3 phase installation we did...
Replies
24
Views
1K
No waffling, going to get straight to the point. Main water on the exterior of the building in plastic. Changes to copper inside the building...
Replies
24
Views
931
I have got these questions on 2391-52 inspection and testing but can't remember option of 1st two questions. Please any suggestion will be...
Replies
2
Views
721

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock