Am I right in thinking that for any ring circuit the maximum value that r1+r2 can be is 1/2 the loop reading on the phase + 1/2 the loop reading for the cpc ( measured at the CU ) Or has my maths let be down?
 
(R1+R2) = (Line loop plus cpc loop)/4.

Doesn't matter what csa cpc is in relation to Line conductor as you are adding the two and dividing the lot by four.

In a ring final circuit you are effectively halving the length of the conductors and doubling the cross-sectional area.
 
Last edited:
(R1+R2) = (Line loop plus cpc loop)/4.

Doesn't matter what csa cpc is in relation to Line conductor as you are adding the two and dividing the lot by four.

Of course it matters......Will the end to end readings not be different for a ring circuit with a 1.5mm cpc and a 2.5mm cpc.

In a 2.5/1.5 ring the yardstick is 1.67 times the the line/neutral end to end value for the cpc.
 
hey len
yeah the end to end readings will vary depending on the ratio of the cpc size
but its still r1+r2 divided by 4

.20r1 + .34r2 /4 = .08 (2.5/1.5)

.20r1 + .20r2 /4 = .10 (2.5/2.5)

i suspect we all know what we mean but its getting lost in "translation";)
 
As Mr Mark Sparks says it is ALWAYS (R1+R2) = (r1+r2)/4 for a ring final circuit. As I say, it makes no difference what csa the cpc is as the equation is still dividing the total of your end-to-end loops by four.
 
The max R1+R2 for a ring final circuit is the maximum value measured during step 3 of the 3 step test. See OSG page 80 - 10.3.2 The formula quoted by others (r1+r2)/4 is only correct for sockets wired on the ring. Spurs will show a higher reading hence the need for the 3 step test to identify spurs and to confirm the ring is correctly wired.
 
IMO the (r1+r2)/4 is only a guide as to what you should get for R1+R2. same as for example if you had a circuit of 10m 2.5/1.5, you would expect R1+R2 to be around 0.2ohms, using the resistvity table 9A OSG. the values entered on a certificate must be measured values.
 

Reply to R1 and R2 Maximum value in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

So I’m doing my level 3 design project at the moment, and I’m on the question where you do all the calculations on each circuit, I’ve taken the...
Replies
3
Views
1K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi All, Had a weird one this morning during an EICR. Testing a ring final circuit in a 2 bed flat… kitchen was on a separate ring. With only the...
Replies
7
Views
1K
Evening everyone, I was taught when carrying out Zs testing to test both L-PE and L-N and record the highest result of the two tests for my Zs...
Replies
11
Views
2K
After fixing a few CPC related issues on a ring final I got the following results L-L = 0.47 N-N = 0.47 CPC-CPC = 0.69 R1+R2 Tested at 0.31...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock