S stevechilts Nov 8, 2010 #1 Carrying out a PIR on a Auto Garage the ring main is wired in metalic conduit with no earth cables what is the calculation to acheive R1+R2
Carrying out a PIR on a Auto Garage the ring main is wired in metalic conduit with no earth cables what is the calculation to acheive R1+R2
IQ Electrical ~ Oct 9, 2010 4,318 1,512 2,688 Nov 8, 2010 #2 You can't calculate it, you can prove continuity via earth loop impedance tests at each outlet and an R2 test if you feel it neccessary. Each outlet must have a fly lead linking it to the metal back box regardless of fixed lugs.
You can't calculate it, you can prove continuity via earth loop impedance tests at each outlet and an R2 test if you feel it neccessary. Each outlet must have a fly lead linking it to the metal back box regardless of fixed lugs.
S stevechilts Nov 8, 2010 #3 Thanks for that, already done the earth loop test and flagged up no fly leads on sockets.