R

Ross1

Hi, does anyone remove lamps when testing R1 + R2 as it says in OSG & GN3.

I`m only getting a 0.02 ohm difference on a 4 light circuit.
 
no, because R1+R2 is across L and E, whereas the lamps are across L and N.
 
Oooh, are you sure Jimmy?

Depends on how you're measuring it.
If you're putting a link between the earth bar and the protective device and measuring at the light you'll be picking up a parallel path through the lamp and Neutral to Earth/Neutral connection on a TNCS or all the way back to the supply transformer on TNS along the Neutral & Earth.

So you'll get a lower measurement.

Try drawing it.
 
Last edited by a moderator:
agree with wirepuller. a lot less effort to dis circuit at CU than pulling out all lamps.
 
That is though lads if you find the right earth that goes with the right Line ................not always easy in a 32 way TP+N+E DB.

On an initial verification you would do your R1 + R2 before you connected to the board, but on a PIR it may be a little different.
 
That is though lads if you find the right earth that goes with the right Line ................not always easy in a 32 way TP+N+E DB.

On an initial verification you would do your R1 + R2 before you connected to the board, but on a PIR it may be a little different.

Along the TP+N+E DB lines, I have a PIR ongoing with 80-100 high bay lights in a warehouse to test. Wondering how many ccts fittings to test etc

ps should I post a new thread in ' Testing. Inspections'
 
Along the TP+N+E DB lines, I have a PIR ongoing with 80-100 high bay lights in a warehouse to test. Wondering how many ccts fittings to test etc

ps should I post a new thread in ' Testing. Inspections'

There are a few factors to this

1 Age of Installation
2. Type of environment
3 Condition of the installation
4 Any previous testing done
5 If any previous testing done what was the results and when was it done.

Obviously a 5 yr old installation is likely not to need as much sampling as a 40 yr old installation that as never been tested, but inversely a poor 5 yr old installation may need more sampling that an excellent 40 yr old one, it is really you judgement and experience when doing a visual inspection at the beginning before you quote for the job.

In PIR work all the training and book study is really a poor second to experience as an experience electrician will within a few hours have a fairly good take on how much work and sampling is going to be needed.
 
That is though lads if you find the right earth that goes with the right Line ................not always easy in a 32 way TP+N+E DB.

On an initial verification you would do your R1 + R2 before you connected to the board, but on a PIR it may be a little different.
Which is exactly why I don't bother with R1 + R2 on a PIR, just Zs.
 
  • Like
Reactions: 2 people
Spin - what do you document as a reason for the LIM in this case? Thanks.
It's not a limitation, as you are not required to record R1 + R2 on a PIR, just to confirm continuity and polarity of conductors.
Obviously you also need to confirm that the Zs are low enough fro the CPD to operate.
 
  • Like
Reactions: 1 person
Thanks Malcolm, I had my few hours assessing the general installation and decided that, in general, a vast majority of the db's (15 of) needed full test and inspection. It,s just a question of the lighting. The storage warehouse is an old 2nd world war munitions factory, no previous test details. It was used previously as some kind of engineering works, with db's added at over the years for various equipment added. Looking at the original lighting system, it is a joy to behold, obviously being designed to a very high spec, and takes me back to my apprenticeship days. However many of the lights are no longer in use or not operating, I would imagine, due to age. So it's a case of time, sorting out an old 10 way db and 30 gang switch system.
What a building though. More steel than the Forth bridge.
 
Sounds like as we would say a pension job, could be there forever.

Obviously the non working lights will come under remedial works and quoted separately from the PIR.

Basically all I would do on a PIR for Hi-bay lighting is IR between L-N to Earth, R2 with a wander lead and Zs at the grid switch.
 
Another week testing. About 150 sq yds, so not massive but double the amount of re-enforcement. took a local builder a week to knock through the outer wall fitting a door. Loads of ccts no longer in use so just disconnecting to remove at source. A lot of damage to various isolators throughout due to dumb stacker truck drivers, etc. May be a point with bonding regarding an external liquid gas supply tank ,still to check. Quite a few damaged overhead crane busbars, all supplies to be removed bar one. That may be a problem.
 
With that liquid gas tank bonding is one thing, but I would also check if the filling point is earthed when it's being refilled, I'm sure it is the drivers are pretty hot nowadays on this.

Sounds like a nice little job there
 
Not bad, but need to keep it tight. The client is a good bloke, good friend of a good friend so I want to do a good job for a fair price, as I usually do, but you know what I mean. He's in the transport business so costs are soaring as with most at pres. You know the situation - smallish businesses, who allows for PIR's on older buildings? Basically it's wait until the insurance man calls, usually after changing provider. Not they're fault but fact and nessessity. Thanks for the advice on the tank. Ian.
 
Last edited:
With that liquid gas tank bonding is one thing, but I would also check if the filling point is earthed when it's being refilled, I'm sure it is the drivers are pretty hot nowadays on this.

Sounds like a nice little job there

Most are as keen as mustard. It’s there neck on the line if there’s spark! Most tanker discharge requires an earth point even for inert products. Mind you it’s funny watching them get a static belt when they haven’t bothered to earth up.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
R1 + R2 Lamps removed?
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
17
Unsolved
--

Advert

Thread statistics

Created
Ross1,
Last reply from
Knobhead,
Replies
17
Views
6,512

Advert