junksamiad

Hi everyone,

I appreciate this is probably a really silly question.

I’ve come across the below test question and although I know how to find the answer, I don’t understand why we would need to know what the max permissible earth fault loop impedance is in relation to a 30mA RCD? I hope someone can offer some simple logic as to why we need to know this?

The question is:
Calculate max earth loop fault impedance permissible for a 30mA RCD used to protect a circuit on a TN-S supply

A. Nominal voltage / RCD trio rating = max earth fault loop impedance

Again, it’s just the theory of reason behind the question that I’m struggling with.

Thanks again as ever.
 
If the EFLI is too high, in the event of a fault the leakage might be less than 30mA and the RCD might not trip. Same as with OCPD but a much higher EFLI is tolerable due to the low current involved. However, FWIW if the EFLI is that high it is likely to be unstable, e.g. if due to Ra of an earth electrode. Therefore, the practical application of this limit is unlikely.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
RCD impedance
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
1

Advert

Thread statistics

Created
junksamiad,
Last reply from
Lucien Nunes,
Replies
1
Views
1,148

Advert