I just follow the series of tests as per BS7671. Can't understand, having completed the dead tests, and securing the cover to the CU, to carry out Zs tests, to then remove the CU lid disconnect the circuits and carry out the RCD test :confused:
PS All appliances/lamps etc, disconnected for all of the tests.
 
i'm with spin on this. RCD might perform perfectly when loads are dissed, but a neutral fault somewhere on the installation could prevent it from operating. the whole purpose of a RCD is to protect against accidental touching of a live part anywhere on the installation. therefore it should be tested as a real life situation, not dissed from the circuits. that's like something working in the lab. but failing in service. tin hat, where art thou?

The circuit should be IR tested before being energised....if you haven't found a N-E fault before live testing shame on you! (;))

I normally test at a convenient point on the circuit rather than at the RCD terminals....simply because it's usually easier depending on connected loads. Newbies need to remember that anything with a capacitor will seriously affect readings and may make a perfectly sound RCD fail the tests.
When it comes to RCBO's it's also the case that some will not respond to a test direct to terminals for some obscure technical reason nobody understands.....these must be tested via the connected circuit,or a couple of short tails need to be connected.
 
Just noting that for all the effort of getting the screw-ins it still means you have to access near live terminals. That said, it's a nightmare holding three leads in the air while pressing a button so those screw-ins are worth their weight.

Why, the ES and SES adaptors are properly insulated and you can plug your insulated leads into them..... or am I missing something?
 
Agree with Tel, long story which I previously recounted (RB explained, I think) earth neutral fault, stopped RCD functioning.
Can't see how. Also struggling to see the point in testing multiple circuits at the end of each when fed from a common RCD? I was always taught to test an RCD at the board, and have always done so.
 
This came up on another thread about a month or so ago. A neutral earth fault may not trip an rcd if the fault decides to use the neutral and not the cpc as the return path due to the cpc resistance.
 
One of the things that will prevent an RCD operating is d.c. current.
This is how the 'no trip' function on MFTs works.
The MFT saturates the coil with d.c. current while it conducts the Zs test.
 
When it comes to RCBO's it's also the case that some will not respond to a test direct to terminals for some obscure technical reason nobody understands.....these must be tested via the connected circuit,or a couple of short tails need to be connected.

It's because a few RCBOs have the current sense coil between the cable entry ports and the terminals (above the location of the terminal screws in conventional vertical orientation) and are sensing the current in the first few millimetres of wire outside the terminals. So if you put your test probes on the terminal screws, you're bypassing the coil. If you probe via the cable entry ports, it'll test OK, but this isn't usually possible due to the space available.
 
It's because a few RCBOs have the current sense coil between the cable entry ports and the terminals (above the location of the terminal screws in conventional vertical orientation) and are sensing the current in the first few millimetres of wire outside the terminals. So if you put your test probes on the terminal screws, you're bypassing the coil. If you probe via the cable entry ports, it'll test OK, but this isn't usually possible due to the space available.

Ooohh, I thought it was something much more complicated!! Makes sense though,thanks for that.
 
One of the things that will prevent an RCD operating is d.c. current.
This is how the 'no trip' function on MFTs works.
The MFT saturates the coil with d.c. current while it conducts the Zs test.
I think you will find nearly all rcds now sense AC and DC which is why the old style of loop tester like Robin (still using one) which used their DLoc technology not to trip the rcd rarely operate through rcds now, this technology used DC which most rcds basically didn't recognise. Modern loop testers use low current of around 10ma so as not to upset the rcd, a method which often supply gives inaccurate results.
 
Can't see how. Also struggling to see the point in testing multiple circuits at the end of each when fed from a common RCD? I was always taught to test an RCD at the board, and have always done so.
I don't know how it does, but it did in my case......keeping it short, connecting up CU & found neutral earth fault on a radial. Decided to investigate that later, and put offending cable to one side, except I didn't and mixed up with another circuit. Carried testing and connecting. Got to testing one of the RCD's & it would not trip under test nor via test button. After a lot of head scratching, went back to the beginning of testing again, but after a short while tested the single 'faulty' cable not connected & realised my mistake. Removed the actual faulty cable from CU, everything hunky dory. Not sure of the science, but that's the reality.

Think either Lucien or Richard came up with an explanation.
 
I think you will find nearly all rcds now sense AC and DC which is why the old style of loop tester like Robin (still using one) which used their DLoc technology not to trip the rcd rarely operate through rcds now, this technology used DC which most rcds basically didn't recognise. Modern loop testers use low current of around 10ma so as not to upset the rcd, a method which often supply gives inaccurate results.
No, only 'B' type sense d.c. current, which is why they are used where there are solar panels.
 

Reply to RCD Test on lighting circuit protected by RCBOs in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

hi all come across a new build commercial office where radial circuits feeding electrak power track was protected by 32A RCBO at dist board and...
Replies
15
Views
1K
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
329
Surely if you fit an RCBO on each circuit, an RCD is not required? Of course, a DP Main switch would be to cut all power, but like I ask, is the...
Replies
3
Views
1K
Hello! I've been racking my brain this evening about some RCD selections. I've been doing some work for a solar installer, and they've asked me...
Replies
5
Views
914
As I've mainly done site work and moved into domestic recently, I'm a bit rusty on stuff like this, but if I'm adding a loft PIV unit to an...
Replies
1
Views
643

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock