no..no and no again.....as a garage socket may be used for outdoor equipment....several ways to deal with RCDs in series....depending on the earthing arrangements
If a TN system then no upfront RCD would be required if you use an armoured cable....you would however use an RCD downstream..(garage)...
If a TT system then a high integrity C/U can be used with a 100mA s type RCD on its own.Then use a 30mA RCD at the garage end....this will give you the discrimination you need.....
Dont panic, was referring to the situation where the house is already covered by an RCD at 30mA, unless the garage cct comes away from rcd protection whats the point if the house always trips first because of other house leakage reducing the threshold of the house RCD.