Got sent this, RCD Failed x1 greater than 300ms maybe if they changed the supply at top of RCD, currently have neutral on the left and line in the right , also the RCD is fed from 63Amp MCB is that all good just feeding an RCBO 30ma board
 

Attachments

  • D5D738F1-C8A6-4261-B22C-A85846766D56.jpeg
    250.5 KB · Views: 42
that's a time delay RCD. and MK RCDs are generally L on right.
 
read mylast post.MK RCDs are normaally that way round.
 
read here:
https://---------------/forums/forum/messageview.cfm?catid=205&threadid=42247
 
Hi - does it trip on the test button or when ramped?
Just FYI, Table 3A has the range of values for 100mA RCDs (and others), non-delayed up to 300ms and S up to 500ms.
 
Who sent you the picture? What was the reason for their visit?
 
Hi guys, my mate sent me it and it’s an upfront RCD for DB in a farm yard (TT) he went through how he tested it as he has brand new tester (Martindale) a similar version to mine and he didn’t flick through the settings and put S which is time delayed, hence why it was saying failed X1 eventually tripped at 310ms so all good
 

Reply to RCD trip time greater than 300ms in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
328
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Replies
13
Views
1K
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
793
A few 30mA RCBO's that i have tested recently are tripping lower at x1 than they are at x5, e.g 13.1 x1 13.8 x5, I know both these results comply...
Replies
12
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock