I'm a homeowner with no electrical skills. BG electrician came to repair something & said my fuse board is not to standard as it only has one RCD. The property was built in 1874 and most of the current systems were put in place in the 1980s. Lived here 24 years & the tripping mechanism works brilliantly. In my basic understanding you can't have two RCDs on one circuit & he was using modern regulations and applying them to my old property, which can't be done retrospectively, am I right? I am trying to sell, will this be an issue on survey & if so, what will it cost to correct. Thanks
 
Hi Claire,

BG engineers, in my experience, put the frightners on people to try and get them to have more work done.

In simple terms, if the RCD covers all the circuits, it's not ideal but unless there is a real need to change it (for other works, new kitchen for example which requires additional circuits say), if someone asked me to replace a consumer unit in such a setup I'd be asking them why and not necessarily writing them a quote.

Yes, we inspect to today's regulations, but that doesn't mean just because it doesn't 100% comply with them that it's not safe for continued use.

Maybe post a picture of your consumer unit and supply intake.
 
The regulations are not retrospective so as long as your installation is in good safe condition for the date it was installed then you do not have to do anything.

The usual reason for having multiple RCDs is so if you have a fault, say, on a socket you don't get plunged in to darkness because the lights share the same RCD. For that reason many houses would now get a dual RCD board.

Also recent regulation changes were to increase the safety by extending RCD protection to most circuits to reduce the impact of accidents such as nailing a buried cable when putting up shelves, etc.

BG do not have a good reputation in these parts, so if you do consider getting a new "consumer unit" (CU, as the fusebox is typically referred to here) then some of the electricians on this board might be able to point you in a better direction.
[automerge]1585920600[/automerge]
When you sell the property is sold has seen
On the electric front if nowt been done recaintly. So I would not be worried if I was you.

Depending on the cost to upgrade and the effect on selling price (or delay in finding a buyer) then it might make sense to upgrade.

But still don't get BG involved!
 
As above BG have a reputation for creating work through unnecessary upgrades. If you have any concerns you can upload pictures of your system here for an unbiased opinion.
 
Hi - I would not worry about it. If it’s raised you may rightly ignore the suggestion (as it’s not a compliance requirement) or perhaps magnanimously offer £50 contribution to an upgrade. Hope you are able to progress your sale at this terrible time ...
 
It's amazing. That BG that goes to house and say your wiring needs up grading or because your boiler needs up grading because we can not get the parts even the boilers are 5 years old its common practice for them to say that, being roborts..
 
Thanks to everyone above for the replies, I feel more reassured about it now. I asked him, hypothetically, if the house needed rewiring (always looking for the worst scenario) how much would it cost and he said £5-£7k ?. I don't know how realistic that is. I like the idea of magnanimously offering £50 Wilko. I was worried it would be a big issue on survey - assuming I ever get to that point given that this scourge is not only delaying everything but knocking house prices down too. ?
 
As mentioned before, if you could post a couple of pictures of your board, meter and main supply fuse we could make more informed comments.
 
The regulations are not retrospective so as long as your installation is in good safe condition for the date it was installed
This isn't strictly true. Regardless of when the installation was erected it will be inspected against current Regulations. Safety issues will be coded as such regardless of whether it was compliant at the time of installation or not. (My usual example is fused neutrals.)
 
This isn't strictly true. Regardless of when the installation was erected it will be inspected against current Regulations. Safety issues will be coded as such regardless of whether it was compliant at the time of installation or not. (My usual example is fused neutrals.)

That is true, but in my limited experience I have only once seen a fused neutral and it was on the incoming supply on what looked like the 1930's era cut-out. That for sure was one cut-out that nobody in their right mind would have tried to pull the fuse! Why the DNO had not replaced it was beyond me, but sadly the lady who's house it was had other problems beyond the dodgy state of the electrics so seemed unable to sort anything out. As far as I know it is still there :(

I think most of a 1980s era installation that was in good condition would be OK, only a few aspects would even make a C2 (potentially dangerous) rating I would expect, such as lack of RCD protection for sockets likely to be used with equipment outdoors, etc.
 
Your best bet would be to get an EICR done by an independent sparky if you’re worried at all. That will give you a view to the age and safety of the installation; and will let you know about any potential problems prior to selling the property.
 
Your best bet would be to get an EICR done by an independent sparky if you’re worried at all. That will give you a view to the age and safety of the installation; and will let you know about any potential problems prior to selling the property.

That is a good suggestion, the paperwork might be need for the sale anyway, and if you do decide to change the CU a lot of the work in doing it properly is in checking the existing wiring (which is why it is considered best practice to start with an EICR).

But as for the work itself, you should find a good electrician to do it. Some companies offer really low prices and do damn-all work for that low money! A proper inspection can take several hours and means unplugging all equipment and removing light bulbs, etc, so the circuits can be fully tested.
 
A proper inspection … means unplugging all equipment and removing light bulbs, etc, so the circuits can be fully tested.
I wouldn't agree with this. Insulation testing between live conductors is something I always agree as a limitation for periodic inspection and testing. I wouldn't entertain carrying it out. And I would certainly claim that I carry out proper inspections - and pick up on an enormous number of issues. Inspection is the primary part of the process. Testing merely supplements inspection, and whilst some issues may be discovered this way inspection is likely to uncover the overwhelming majority.
 
I wouldn't agree with this. Insulation testing between live conductors is something I always agree as a limitation for periodic inspection and testing. I wouldn't entertain carrying it out. And I would certainly claim that I carry out proper inspections - and pick up on an enormous number of issues. Inspection is the primary part of the process. Testing merely supplements inspection, and whilst some issues may be discovered this way inspection is likely to uncover the overwhelming majority.

I don't agree on all of that. Yes, the inspection is very important (as it is for PAT testing but often overlooked). It gives you the majority of age or use-related degradation that way, should show some of the C1 faults (exposed conductors, etc) and it also give you a good insight to the original installation quality (or lack thereof) and any subsequent work.

But...I have to say that I believe testing if also a fundamental aspect: "that will never happen" polarity reversal, looking for open conductors on rings (or imbalance pointing to poor joints), looking for linked or "shared neutral" circuits, and checking for signs of insulation degradation from mice chewing or otherwise damp/bad insulation, checking that Zs is low enough to be reasonable so you have some confidence in the condition of junctions/terminals, etc.

Now you don't have to remove everything for a good insight. You could do testing with L+N -> E to save unplugging or bulb removal and it will give you most of the information you could expect to get from such a test more easily, and without risking electronic devices that are still attached (as you could with a 250V test instead of 500V), but I still believe in testing.

Apologies to the original poster - we don't want to hijack your thread to discuss views on EICR, but that sort of thing can happen!
 
I wasn't suggesting that testing isn't important. I was simply stating that the inspection is more fundamental and is supplemented by the testing. (Again - I'm not suggesting that testing is unimportant.)

I almost never insulation test at 250V really. One of the few reasons to do that would be where there is an SPD, but these are easily removed.
 
If you carry out a thorough inspection, you should be in a position to assess the state of the existing wiring and decide, as a result, how far you need to go with IR testing.
 
Thanks to everyone above for the replies, I feel more reassured about it now. I asked him, hypothetically, if the house needed rewiring (always looking for the worst scenario) how much would it cost and he said £5-£7k ?. I don't know how realistic that is. I like the idea of magnanimously offering £50 Wilko. I was worried it would be a big issue on survey - assuming I ever get to that point given that this scourge is not only delaying everything but knocking house prices down too. ?

I would doubt much, that a prospective house sale is going to get going on any estate agents books, in the current crisis. So sit tight and wait at home.

If your house needs electrical refurbishment, that may be reflected in any offers by your buyers. I would not bother with any prior electrical inspections, unless there are obvious concerns for safety. Allow your buyers to negotiate survey's etc during the sale process, should that subject even rise.
 
The issue of EICRs during a house sale is a thorny one. I've recently had cause to go and look at an installation that the seller's EICR claimed was safe and satisfactory.

The EICR was used to mask an un-notified board change (to install RCDs because the original surveyor commented on the lack of RCD protection). The quality of the work was horrendous but because the EICR said satisfactory they proceeded with the purchase. It wasn't until a family member (my AM2 assessor) went to carry out some works that this came to light, he then asked me to go and take a look.

My advice to sellers is that unless you have genuine concerns about the safety of the installation, don't do anything. Let the buyers shoulder the cost, but keep in mind that the buyers spark may be under instruction to 'get us a reason for dropping the price'. They may also be the kind of spark who finds things wrong to generate work.

If the buyers report comes back as unsatisfactory, it might be worth having a spark you trust (recommendation from family, friends, have previously used etc.) spend an hour with the report and the installation to double check the report. I was quickly able to establish the EICR from the seller wasn't worth the paper it was printed on and that's given the buyers some ammunition in trying to recover the cost of having the place rewired which is what it really needs (whether that will succeed or not is another matter but two electricians have visited the property on their behalf and found it to be sadly lacking and not at all as described on the EICR).

It's also worth pointing out that an EICR can have observations on it and still be satisfactory. Observations are classified as C1 (Danger present), C2 (Potential danger - i.e. something has to happen for the issue to become dangerous), C3 (Improvement recommended) and FI (Further investigation). Any C1, C2 and FI observations will result in an unsatisfactory EICR. So if the report has C3's only, this is no reason to drop the price as the EICR should be satisfactory (i.e. safe for continued use).
 
BG are awful. They trade off the historic name and reputation but the prices they charge and work they justify is often suspect.
A lot of it isn't even carried out by them but subbed out to other firms. Often the lowest bidder or on fixed price work per job.
So corners are cut to maximise profit.
If they tell you to get work done then get other quotes and don't use BG.
Personally I think, it's about time they get exposed on rogue traders again as they haven't learned.
[automerge]1586014309[/automerge]
The issue of EICRs during a house sale is a thorny one. I've recently had cause to go and look at an installation that the seller's EICR claimed was safe and satisfactory.

The EICR was used to mask an un-notified board change (to install RCDs because the original surveyor commented on the lack of RCD protection). The quality of the work was horrendous but because the EICR said satisfactory they proceeded with the purchase. It wasn't until a family member (my AM2 assessor) went to carry out some works that this came to light, he then asked me to go and take a look.

My advice to sellers is that unless you have genuine concerns about the safety of the installation, don't do anything. Let the buyers shoulder the cost, but keep in mind that the buyers spark may be under instruction to 'get us a reason for dropping the price'. They may also be the kind of spark who finds things wrong to generate work.

If the buyers report comes back as unsatisfactory, it might be worth having a spark you trust (recommendation from family, friends, have previously used etc.) spend an hour with the report and the installation to double check the report. I was quickly able to establish the EICR from the seller wasn't worth the paper it was printed on and that's given the buyers some ammunition in trying to recover the cost of having the place rewired which is what it really needs (whether that will succeed or not is another matter but two electricians have visited the property on their behalf and found it to be sadly lacking and not at all as described on the EICR).

It's also worth pointing out that an EICR can have observations on it and still be satisfactory. Observations are classified as C1 (Danger present), C2 (Potential danger - i.e. something has to happen for the issue to become dangerous), C3 (Improvement recommended) and FI (Further investigation). Any C1, C2 and FI observations will result in an unsatisfactory EICR. So if the report has C3's only, this is no reason to drop the price as the EICR should be satisfactory (i.e. safe for continued use).
I have seen a lot more cases locally of EICRs being carried out and then an indemnity policy arranged by the sellers solicitors (around £100 for a semi through to over 2k for a Georgian town house) to progress the sell. The downside to that is you better make sure the EICR is water tight as if its not the insurer will come knocking on your door first if there are issues later on.
 
Last edited:
Is there any actual evidence of insurance companies pursuing contractors on that basis ?
Not heard of it but when you are talking about listed Georgian townhouses worth between 1 and 5 mlion pounds. You can be certain if something did come to light given the potential costs the insurer would look to persue a case against the indemnity policy and then the electrician in turn hence professional indemnity. When I did a EICR for a substantial townhouse last year which took 4 days to do. I had to get an additional cover provision to my professional indemnity for £5m coverage at request of the customer and his building insurer. Added the extra cost to the invoice. As my PI covers 500k normally. With all these things it's a worse case scenario thinking but at some point somebody will come unstuck with these poor EICRs.
 
And what is that supposed to mean? indemnity insurance is just that it indemnifies the insured up to the amount of the insurance for claims against them.
It means exactly what it says.I had a job recently the customer had no eic for new Circuits and no original spark to ask for one. I told him about ins policy optoon and the other solicitor would not accept one ended up with an eicr
 
I'm sorry I still don't get what you are trying to say?
If the seller of a property has had electrical work done and no paperwork to back it up then an indemnity policy mIght not get accepted .if the buyers solicitors for whatever reason won't accept one . Only saying because it happened to someone I know recently
 
I still don't get it, the Professional indemnity insurance policy is taken out by the electrician not the seller of the property, I don't get the bit about the buyers solicitor not accepting "one" one what?
 
Think we are at cross purposes.

There's Professional Indemnity Insurance for trades persons etc, to provide them with cover should it be alleged to have provided inadequate advice or service.

And there's Indemnity Insurance a type of protection, purchased during housing transactions. It is a one-off payment for a policy that then lasts forever. It is used to offer protection if there is a potential problem with the property that could result in local council action or legal problems in the future.

Note, the later does not remedy the insured defect.
 
Think we are at cross purposes.

There's Professional Indemnity Insurance for trades persons etc, to provide them with cover should it be alleged to have provided inadequate advice or service.

And there's Indemnity Insurance a type of protection, purchased during housing transactions. It is a one-off payment for a policy that then lasts forever. It is used to offer protection if there is a potential problem with the property that could result in local council action or legal problems in the future.

Note, the later does not remedy the insured defect.
Thanks Midwest that's better
 
As I have said before, an indemnity policy purchased during a house sale to "cover" some defect is increasingly popular, especially amongst lazy lawyers. The policy does not cure the defect, it only provides monetary compensation in the event of a subsequent problem.
Historically they were used to cover problems with the title to the property, whereby some 3rd party might challenge the title. Thereafter the insurance companies offered them to cover situations where alterations had been done without Building Warrant or other consents. In the main, they are pretty useless. However, as above, the purchaser/his solicitor is under no obligation to accept such a policy, so it follows that even if the current purchaser does go ahead, a subsequent purchaser from him may not. Thus, they are a last resort, in cases where the risk is minuscule. A good and proper title needs no fortification.

Many lawyers are using these policies as a simple way to make problems go away. That is poor practice. Also, if a lender is involved, they have to be consulted over an indemnity policy, and often they will fire it back to the lawyer and say they will follow his advice. Neatly, that means that the lawyer himself, as well as the insurer, is liable in a claim if the lender loses out...and that is where the lawyer's Professional Indemnity insurance kicks in.
As the condition of an electrical installation is not (yet) a factor in conveyancing transactions here in Scotland, the (very) few insurers who offer indemnity for house purchase matters have not yet had to concoct another load of convoluted drivel to make it look as if they are covering the "defect"even if in reality they are not. This is a good thing. These policies were originally known as Defective Title Indemnity policies, and that is what they should remain-policies that offer some financial compensation for a defect in title to the property, not for some dodgy wiring. Title defects are usually cured by passage of time, dodgy wiring is not.
 
Thanks for the clarification chaps, it's no wonder I was at cross purposes, MultiMick replied to my post on the EICR and this indemnity is nothing to do with the electrical installation or the electrician.

I think the crux of any purchasing Indemnity is the words "third party" the seller being the first party and the buyer being the second party, the third party is someone or an organisation outside the selling and buying process.
 
As my PI covers 500k normally. With all these things it's a worse case scenario thinking but at some point somebody will come unstuck with these poor EICRs.
I said this in a previous life on this forum and I'll say it again as I honestly believe people completely misunderstand the extent of what an EICR is capable of highlighting.
On all but very small installations 100% inspection is not realistic and anyone who claims 100% is lying or deluded. Removing hundreds of points and accessories would be excessively time consuming and impose an unacceptable cost burden on the client. It would also cause unacceptable damage to surface finishes and almost certainly introduce faults that were not previously present. The more disturbance the higher the risk. For that reason it is recommended that a percentage of points are removed for inspection, typically around 25% would be considered adequate, with the sample being increased if defects are identified. If no or insignificant defects are observed then 25% sampling will likely be deemed adequate, which also means 75% of points will not be properly inspected. If a potentially dangerous defect is present in that 75% then it may not be identified.
If following such an EICR a fire or electrocution results from that defect then everyone on this forum will be talking about dodgy EICR's and cowboy electricians, when in fact that scenario could befall ANY competent electrician on this forum.
Think on.
 
I always though the sample inspection was more about determining the general quality of the original work than anything else. As you say doing 100% opening for inspection is utterly impractical.

But inspecting the outside appearance of near-100% is feasible and very valuable in case of damaged/burned examples, even if some are going to be behind washing machines, etc, and difficult to include (but ironically probably more important given the high load).

Similarly if you had doubts then I guess PFC/PSSC on each socket could be measured at a tolerable cost and risk, and that might show up poor connections (or more likely dodgy sockets), as a ring loop R check can also point to such things.
 

Reply to RCD x1 on fuseboard in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Grateful for your expertise regarding my confusion on the below. Context: French rural domestic property Single phase supply, TT...
Replies
12
Views
2K
Hi, I recently had an EICR done at my property which unfortunately was unsatisfactory. So the electrican advised a new fuseboard from BG General...
Replies
90
Views
4K
Hello. we have had a few powercuts over past few months and am in middle of one at the moment where power has gone off a few times while DNO are...
Replies
8
Views
4K
I've got a bunch of old single phase BS88 1970s fuseboards in the communal areas of a converted building. All the wiring is MICC and it's buried...
Replies
9
Views
1K
Hi, I am a basic DIY'er, with basic electrical skills, NB, I can change a plug/fuse, change a ceiling light fitting, change a socket face plate...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top