Hi all,

I've tried searching but every time I hit the 'search' button, it takes me out of the forum!

Set up: 6-way consumer unit (changeover). 30mA rcd controlling 4 power (32+32+16+40) mcb's + 2 6a rcbo's for lighting.

I've done all the testing. Voltage 247v. Everything fine but....

Upon testing the RCD,it trips 10.2mA @ 1I, and 8.4mA @ 5I
And the rcbo's ... 18.2mA @ 1I and 18.1mA @ 5I

Can I have some help in understanding what's going on. I know it's the rcd/rcbo combination (cause I changed it all for a straight 6-way unit with ONE rcd and then the results were as expected I-30.2mA & 5I-6.9mA ...)

thanks,

Stewart
 
Im with m4tty here, i dont understand what question you are asking, you have shown us a set of results that have passed so what is the question, are you confused that the x5 results should be a fifth of the x1? this isnt the case and this rarely is the case, to pass it just has to trip within the specified times thats all, existing leakage, load, voltage etc will all play a small part as to the result but as long as they meet the regs then all is good.
 
Well there you are then, all safe and sound :)

Hmmm, yes I was confusing the mA with the mS lol ..... put it down to a hard day and refusing to think clearly! Shall just go off and write out 5,000 times - "I must not write in to forum when thinking like a plumber!" ..... 5,000 lines later...... sigh! that's better, I shall go and make myself a nice cup of tea :) :)
 
Have you tried testing the RCD on its own ? because this will prove if it is the RCD or maybee you have some leakage on your installation
 

Reply to RCDs in the Australia area at ElectriciansForums.net

Similar Threads

Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Replies
19
Views
1K
Hi. Not sure if it's the right place to ask, so won't be upset if it gets removed. Apologies if the terminology (PEN/PME/etc) is used...
Replies
44
Views
7K
Hi all,looking for some pointers to an RCD problem, I work entirely on large poultry farms, I've only been in post a year, at some point before I...
Replies
6
Views
2K
Having a bit of a brain freeze moment. I have a 2-core SWA cable running to an outbuilding. The sheath is used to earth this cable back to the...
Replies
1
Views
1K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock