I have 3 locations that have a relay controlling a pump, each site is several miles from each other and when my SCADA system calls for RUN all three relays energize at the same time. What I need is a local control that allows only 2 pumps to run at the same time but they need to alternate, (example) 1&2 when called then 1&3 on next call then 2&3 then back to beginning. Each site has a 12vdc relay interrupting the Auto of a selector switch, I was thinking of alternating relays for the control circuit but would like help in a wiring diagram showing this solution.
 
I have 3 locations that have a relay controlling a pump, each site is several miles from each other and when my SCADA system calls for RUN all three relays energize at the same time. What I need is a local control that allows only 2 pumps to run at the same time but they need to alternate, (example) 1&2 when called then 1&3 on next call then 2&3 then back to beginning. Each site has a 12vdc relay interrupting the Auto of a selector switch, I was thinking of alternating relays for the control circuit but would like help in a wiring diagram showing this solution.
dconner since it’s pumps I’m assuming that you have motor starters which should have 2 sets of dry contacts with 1 being NC and the other NO. Having said that you could use the auxiliary contacts to stop any motor from starting. I can’t draw you a wiring diagram on my phone. I would see if you can do that without adding another relay. Good luck
 
dconner since it’s pumps I’m assuming that you have motor starters which should have 2 sets of dry contacts with 1 being NC and the other NO. Having said that you could use the auxiliary contacts to stop any motor from starting. I can’t draw you a wiring diagram on my phone. I would see if you can do that without adding another relay. Good luck
I failed to mention the control relays come on from a Digital Out on my RTU, this being said I need to locally make each location skip a command on cycle thus the need for a alternating relay. In essence each location has a wireless controller that all receive the command on. The issue is how can I make the sites come on in this sequence. 1&2 2&3 1&3
 
I failed to mention the control relays come on from a Digital Out on my RTU, this being said I need to locally make each location skip a command on cycle thus the need for a alternating relay. In essence each location has a wireless controller that all receive the command on. The issue is how can I make the sites come on in this sequence. 1&2 2&3 1&3
So you are controlling 3 motors off of one output and with a wireless command and I’m guessing you can’t change the logic on your RFU. It can be done with external relays and possibly a timer but I have to see if I can come up with a wiring diagram for you
 
I have 3 locations that have a relay controlling a pump, each site is several miles from each other and when my SCADA system calls for RUN all three relays energize at the same time. What I need is a local control that allows only 2 pumps to run at the same time but they need to alternate, (example) 1&2 when called then 1&3 on next call then 2&3 then back to beginning. Each site has a 12vdc relay interrupting the Auto of a selector switch, I was thinking of alternating relays for the control circuit but would like help in a wiring diagram showing this solution.
What size pumps and voltage are we talking about. Is these 3 phase motors?
 
Two out of three pumps running simultaneously means that each pump has to miss every third start. The sequence has to be 'launched' with each pump's counter at a different point in the cycle and one has to rely on them always receiving the start commands to avoid them getting out of step. If one counter misses a start, one, two and then three pumps will start at each successive command until the cycle is corrected manually.

Thought: Does the pump duty rota have to change every start or can it be time-controlled, so that each pump misses every third day or hour? Does it matter if there is occasionally some overlap, e.g. if a pump is already running at duty changeover time? How frequent are the starts? Is the SCADA output momentary or is it active all the time there is demand?

If the sequence needs to advance at every start, then yes it can be done with a couple of relays or electronic counters or all sorts of different ways.
 
Two out of three pumps running simultaneously means that each pump has to miss every third start. The sequence has to be 'launched' with each pump's counter at a different point in the cycle and one has to rely on them always receiving the start commands to avoid them getting out of step. If one counter misses a start, one, two and then three pumps will start at each successive command until the cycle is corrected manually.

Thought: Does the pump duty rota have to change every start or can it be time-controlled, so that each pump misses every third day or hour? Does it matter if there is occasionally some overlap, e.g. if a pump is already running at duty changeover time? How frequent are the starts? Is the SCADA output momentary or is it active all the time there is demand?

If the sequence needs to advance at every start, then yes it can be done with a couple of relays or electronic counters or all sorts of different ways.
Thanks for your help Lucien ?
 

Reply to Relay wiring assistance in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Good day to you. I need electrical drawings urgently and hopefully there is someone that can assist me. They are all for electrical trade test...
Replies
6
Views
790
Hi all, Looking for someone to help with this dilemma. Image attached to try and explain it better. We have 3 separate lights currently...
Replies
3
Views
605
Hi all I am new to this forum and hope this is right placed and of interest. I would like to make a setup with one or more impulse relays...
Replies
9
Views
1K
Hi all, I need help/feedback. I am modifying a machine. I have added an aluminium profile frame (enclosure ) to a machine (the machine will be...
Replies
2
Views
789
HI, Hoping someone can help me here as I am a novice. This is on a vehicle so I hope thats ok but I think it pertains. Long story is I have a old...
Replies
1
Views
600

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock