Thanks for your opinions/guidance guys, i think i may have been too stuck with the routine of noting 'non compliances to current edition' that was a C4 from the old periodic inspection reports!!!!!!!
so.....generally you wouldn't note the plastic consumer unit provided it is in good serviceable condition etc?
 
The Electrical Safety First Best Practice Guide 4 (issue 4) has clear guidance on coding (or not) plastic CUs:

Page 16, example of C3:

For inspections carried out after 1January 2016 - Presence of a consumer unit or similar switchgear made from combustible material (e.g. plastic) that is not inside a non-combustible enclosure and which is:


  • Located under wooden staircase, or
  • within a sole route of escape from the premises

    (Note: If unsatisfactory connections are found during inspection, this would warrant a code C2 classification to be recorded)

Page 17, Items worthy of note that do not warrant a classification code (These comments would not appear on the EICR):

For inspections carried out after 1January 2016 - Presence of a consumer unit or similar switchgear made from combustible material (e.g. plastic) that is not inside a non-combustible enclosure and which is NOT:


  • Located under wooden staircase, or
  • within a sole route of escape from the premises

    (Note: If unsatisfactory connections are found during inspection, this would warrant a code C2 classification to be recorded)

The following list of FAQs is also useful: Inspection, testing, certification and reporting - http://www.electricalsafetyfirst.org.uk/electrical-professionals/wiring-regulations/inspection,-testing,-certification-and-reporting/
 
More of a space issue. Getting rcbos in older boards can be a pain. Also if there is no sup bonding in the bathroom and a shower in place with no rcd protection, this would be a c2. So there are still cases were not having an rcd can result in a eicr fail. I hate doing work for landlords. Most of them just want the bit of paper saying it's safe with out actually caring if it is or not.
 

Reply to retro fitting rcbo's into a non amd 3 board in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

2 questions.. 1. Will the mini Starbreaker RCBO's fit in this board? Below is a picture of the board and also the type of RCBO I want to fit in...
Replies
3
Views
360
So here is the thing Rhere is an old MEMSHIELD TPN+E Board that is pretty mich obsolete. The only place that sells their breakers would be Ebay...
Replies
5
Views
915
I had a call to a new customer who was experiencing what sounded like nuisance tripping on a kitchen ring. Some background first. It's an MK LN...
Replies
4
Views
792
Just to be clear… I am going to do the correct thing here and pay for the correct parts…. I just wanted to start the discussion. My particular...
Replies
6
Views
332
Hi All I'm new here. I have just finished my NVQ and waiting to do my AM2. I have a question on selectivity as it has always slightly confused me...
Replies
5
Views
844

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top