Hi All,

While carrying out a commercial EICR today, I was doing IR testing on one of the ring mains an was getting 0.00M ohms between L/N - and the earth bar at 250V & 500V (cant distinguish what 2 earth wires belongs to the other 4 cores)

I have continuity on both L & N legs which are acceptable.
Also tested L- E bar and N - E bar both giving me 0.00M ohms
carried out a resistance test for both L & N to E bar, one was 24.4 ohms and the other was 1034 ohms

No RCD protection at all. TN-S system.

Stumped.... any suggestions on coding and where to start looking for this would be greatly appreciated.

when you i.r tested at 250v and got an unsatisfactory reading why did you then test at 500v ?
 
Ok
1. 500V is the standard test voltage for pat testing, if anything can be damaged by 500V current limited to 1ma then it shouldn't be plugged in as it would fail the type testing
2. The output of a megger is current limited to about 1mA so it can't power anything.

The 500V from a PAT tester is applied with the live and neutral connected together, not applied between live and neutral. Daz
 
  • Like
Reactions: 2 people

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Ring main IR question from todays EICR
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
21

Advert

Thread statistics

Created
Ross1,
Last reply from
DPG,
Replies
21
Views
3,274

Advert