Hi All,

While carrying out a commercial EICR today, I was doing IR testing on one of the ring mains an was getting 0.00M ohms between L/N - and the earth bar at 250V & 500V (cant distinguish what 2 earth wires belongs to the other 4 cores)

I have continuity on both L & N legs which are acceptable.
Also tested L- E bar and N - E bar both giving me 0.00M ohms
carried out a resistance test for both L & N to E bar, one was 24.4 ohms and the other was 1034 ohms

No RCD protection at all. TN-S system.

Stumped.... any suggestions on coding and where to start looking for this would be greatly appreciated.
 
Hi Ross.

I know it may sound obvious but did you have the main switch off when you were testing (not just the MCB) as it is TN-S so will be continuity between N and E (and also L-E unless you were sure everything was unplugged?).

If the main switch was open when you tested then I guess you have an earth fault somewhere (commonly a screw in one of the back boxes clipping the neutral). As this is an EICR I would just be coding it and not thinking too much about solving the fault yet (unless you code it C1).
 
Last edited:
Yes HHD, the main switch was open..both lives out of MCB, both neutrals out of the neutral bar. The earths all still in earth bar. I know the likelihood is that the fault is down between both live conductors and their own cpc. All other ring mains were all >500Mohm apart from another which had a reading of 0.40Mohm.

circuit working fine....although no RCD is present. So I'm thinking a C1 or 2
 
What was the actual measured resistance?
0.00M ohm could mean the actual measurement was 999,999ohms.
I'd be inclined to say there is a load still connected, or a neon or PIR somewhere on the circuit.
 
Hi Alanl, the resistances are in my original post. This would surely not be the case though as I was doing IR between live/neutral to earth
 
TNS with the main switch closed would still give a N-E resistance of 0.0MΩ, the connection is just further away (at the sub station).

I would say that you have a 52W piece of electronics still connected.
The smoothing capacitors giving you the 24Ω L-E reading as a false reading and the 52W coming from the difference in the N-E resistance to the L-E resistance, so the N-E is 1010Ω higher i.e. 52W
 
Ok
1. 500V is the standard test voltage for pat testing, if anything can be damaged by 500V current limited to 1ma then it shouldn't be plugged in as it would fail the type testing
2. The output of a megger is current limited to about 1mA so it can't power anything.
 
The smoothing capacitors giving you the 24Ω L-E reading as a false reading

Not sure I get your meaning here. No capacitor (except a failed one) should affect a reading on a DC insulation test, although suppressors legitimately create AC leakage when energised. Smoothing capacitors would never be connected in any way to E as they are part of the current-using equipment. Did you mean varistors? They might give an unduly low reading L-E at 500V but not at 250, and would look open-circuit to the continuity test.
 
Last edited:

Reply to Ring main IR question from todays EICR in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
800
So I’m an apprentice and I’m just trying to get a better understanding of the science behind this because the electricians who have said it have...
Replies
12
Views
1K
Recently changed a CU for a friend and today when visiting one of the RFC's RCBOs tripped. It was due attention anyway as open ring and no time to...
Replies
13
Views
1K
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
609
Over the last few days, I have stumbled across a number of threads that seem to point to a prevalent misunderstanding. Either that, or I have been...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock