why do people run a cpc Along side the armoured that supplies the board. Why not use the metal sheathing as the earth?
 
One reason could be that the SWA is susceptible to rust and corrosion and over the life time of the installation the integrity of the earth could become compromised.

Another reason could be that the SWA is not sufficient in terms of equivalent CSA size to carry the fault currents or meet bonding requirements.
 
  • Agree
Reactions: Pete999
why do people run a cpc Along side the armoured that supplies the board. Why not use the metal sheathing as the earth?
The armour may not be of an adequate CSA. The armour may not be of an adequate CSA for bonding (if bonding is required). Long runs may have a seperate earthing conductor to meet disconnection times. In areas like marinas then the armour should not be relied on due to corrosion.

Edit:@DavidSpark beat me to it :)
 
Looking at this table it shows there all more than capeable. This is why it’s confusing me. Lol
 

Attachments

I think it all comes down to what the designer specifies most of the time. If my name is going to go onto something then I'd like to know that it's going to be rock solid.

Peace of mind is something you can't put a price on, if god forbid something went wrong and they eyes and fingers come looking for you.
 
Looking at this table it shows there all more than capeable. This is why it’s confusing me. Lol
Not all of them are capable Steve look at the cables shaded in pink.
 
Not all of them are capable Steve look at the cables shaded in pink.
But I’m on about a standard 3phase board now if they are 25mm (most are) then why run it? Is it due to resistance of copper rather than steel?
 
But I’m on about a standard 3phase board now if they are 25mm (most are) then why run it? Is it due to resistance of copper rather than steel?
The armour of a 25mm SWA would not be adequate for bonding.
 
  • Agree
Reactions: Pete999
But I’m on about a standard 3phase board now if they are 25mm (most are) then why run it? Is it due to resistance of copper rather than steel?
Perhaps if you had mentioned that in the first post then there would have been less confusion, 25MM4 core SWA has a steel csa0f 70mm2 equivalent to 22.5 mm2 copper, but as others have said that wouldn't be good enough for bonding as well as a cpc, of course only if bonding is required.
 
  • Like
Reactions: uksrevivor

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Email
Joined
Time zone
Last seen

Thread Information

Title
Running cpc with swa and not use the swa as cpc
Prefix
N/A
Forum
Electrical Course Trainees Only
Start date
Last reply date
Replies
8

Thread Tags

Advert

Thread statistics

Created
Steve93,
Last reply from
Pete999,
Replies
8
Views
166

Advert