My pal has asked for a power supply for lights and sockets in his garage and so can I just ask if the following would be ok ???

32A MCB at the main CU to protect garage feed.
2.5mm SWA run of 30m to the garage
Secondary CU in garage with 1 20A radial for 3 socket outlets and 1 6a lighting circuit.

considering volt drop over this length would I need to up the SWA to 4mm or should 2.5 do ??

cheers
 
Just a quick point here on the discrimination of RCDs.
If you have an RCD at source and then also at the secondary DB, then I reckon you need a time delayed one at source so that if there is an earth fault on one of the garage circuits then the RCD nearest the fault will trip.

However, If you've got a time delayed RCD at the main CU, does that still meet all requirements of additional protection for the other circuits connected to the main CU? I'm guessing it does ?
 
Easiest way, if it is possible, is to arrange the house CU so that the distribution swa is not protected by an rcd and just have the rcd in the submain.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
secondary DB !!!
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
7
Unsolved
--

Advert

Thread statistics

Created
Murdy,
Last reply from
pushrod,
Replies
7
Views
1,719

Advert