Discuss Shower tripping mcb after being used in the UK Electrical Forum area at ElectriciansForums.net
Hello. Can anybody please help. I've been in my house for 5 years and had no trouble with shower at all. A couple of weeks ago the wife says that shower wasn't working. I looked at circuit board and mcb had tripped. Flicked switch back on and everything was ok. Went for a shower later and its tripped again. Flicked it back on and it worked again. Thought shower might be knackered with being old so put a new shower in. 8.5kw with 32a mcb. Same problem.
I can flick mcb on and it will stay on, I can have a shower and it stays on, when I turn shower off it still works but a few minutes after I turn shower off it trips mcb. Any ideas off what the problem is will be greatly appreciated. Thanks
Is it the same 32 amp MCB that you have always had? If it is then it could be getting tired.A 8.5kw shower can pull approx 38 amps which is stressing the 32amp mcb.Over time they get lazy and trip even more.I would recommend changing the mcb to a 40 amp and see how it goes.Don't forget that since Jan 1 ,the replacement mcb has to be the same make and model as the original.You can usually source one off Ebay if your local wholesalers doesn't have one.
Hi V and Welcome to the Forum!
I suspect you're going to need some help to fix this as it could be a wiring fault (is it mcb or rcbo?) or a tired mcb as per Bob.
Whilst the advice on the mcb made be reasonable, who is to say the cable is big enough?
Unless you have competence and test kit, rushing to upgrade a mcb could have unpleasant consequences ....
It's a fixed load, changing the mcb for a higher rating will have no effect on overload protection, which is not required, only fault protection will be affected.
agreed, but OP needs to determine if the cable is the correct size for the load, ref. method being taken into account.
Thanks for the advice. I believe the current mcb is a Lewden one. Does that mean I have to get it swapped with another lewden. Why can i not use something like a Wylex if it's the same ampage
Have you read post #7?
And no you can't fit any manufacturer .... some won't fit at all and we are now on the 18th edition which specially stops it
As above, it is now a departure from the regulations to fit a device from a different manufacturer, unless you want to be legally responsible for the design of your DB if a fire was caused.
On about upping the cable size to suit the protective device, though.
Hi - my best advice is to get someone in to help you fault find. You should not be opening up your consumer unit and changing circuit breakers, just saying.
It's a fixed load, the load will be 8.5kw regardless of the rating of the protective device. Overload protection is not required, only fault protection.
Matters not. I am not saying up the breaker.....but if you do up it, the cable should also be upped accordingly for cable protection. That protection is needed, even though you are not varying the load. Just regulation, that's all.
I wouldnt fancy showering under a electric shower that's tripping the mcb.
Get the circuit tested, rcbo fitted and replace the shower if necessary.
Reply to Shower tripping mcb after being used in the UK Electrical Forum area at ElectriciansForums.net
I'm not sure what's going on with my kitchen light. I've replaced an old 28W CFL fitting with a new 4 x LED GU10 fitting (a cheap one from...
Went back it a house after they upgraded shower to a 9.8kw, pulling 40a constant. We had wired it with 10sq and 40a RCBO. 10sq Neutral cable...
Can i just check something. If a rat decides to chew a cable will it trip the MCB or RCD ? I ask because I had one house recently that had a...
90s house electric issues continues 🥲 So after getting some good advice here I've managed to sort out some of the heating issues so thank you...
I have a 32amp MCB for my heating (heat pump) and when the heating comes on, it trips after a few seconds. If I push it back up it works fine...