I can tell you that the same process should be carried out as for domestic premises, but that’s simply from following the regulations and we’ve already established you’re not keen on that.

To clarify, that’s 443.4 where single dwellings are excepted from the requirements to perform a risk assessment. You need to carry out a risk assessment or if you decide not to carry out a risk assessment you need to provide transient overvoltage protection.
 
Last edited:
I recently had a similar question. Part of my journey towards the answer in my particular case was this short article:
 
So what the guidance is saying Johnboy, do a risk assessment of clients electronic equipment (cost)and ask them isit worth it or not.

They should sign it too.
 
I agree with @Doomed
In many cases if you cost the time to perform the risk assessment and go through the options with your client (including getting the value of equipment they have that is susceptible to damage, and the cost implications of lost business due to damage-induced down-time, etc) it will cost about the same as fitting a type 2 SPD anyway!

Edited to add: If they have a lightning protection system to need type 1 SPD then it has to be fitted anyway. Though some remote sites with lots of lightning activity might be better served with a type 1 so it lasts longer.
 
What happens if their electronic equipment still goes bang in a lighting storm
Their problem, as you have done your bit.

Most electronics should survive at least the CAT-II sort of surges, but some are simply crap, and others are also vulnerable to damage though data lines (cable TV coax, phone line, etc) so would need separate protection.

You can harden electronic installations to survive a direct hit and keep going, but not domestic installations for sure!
 
Have other services as phone, cable tv adopted this too?
Don't know about cable TV, but traditional phone lines always had SPD at the master socket and there are standards for the sort of spikes that telecoms stuff should handle.

Though I suspect that has gone from newer systems. Probably BT, etc, treat the modems as disposable - they often don't update the crap software anyway!
 
From the archive of "here is one prepared earlier" we installed a system in Italy in 1995 and upgraded its computers and radio part in 2005. In 2019 I went out to repair it as they said it stopped working in one of its frequency bands, but the antenna was still tracking and working in the other.

Only later did they admit that it happened at the same time as a lightning storm.

Then when I got there and took down the front-end (bit that sits at the focus of a dish-style antenna) to replace the failed low-noise amplifier I found this melted spot where it actually had been hit:
IMG_20190129_173140773.jpg


Here is a photo of what that metal cover has inside:
IMG_4623.JPG
 
We had put some effort in to protecting it against induced lightning surges, but never thought it would have survived a direct hit!

This was not really planned for, and the bureaucracy of trying to get the institute to fit some protection (and find the budget to do so) was a problem. The building itself was protected, but the antenna was now the highest point.

So we made up a makeshift LPS using stuff from local hardware shops, in between ice-creams and coffees, and hopefully it will be OK for the future:
makeshift-lightning-protection.jpg
 
What happens if their electronic equipment still goes bang in a lighting storm
In a commercial set up the installation should be set up in zones, each one designed to step down the surge current to a tolerable level at the equipment.

MDMImage.png


Same can be applied in domestic by using type 3 surge protected outlets.
 
We had put some effort in to protecting it against induced lightning surges, but never thought it would have survived a direct hit!

This was not really planned for, and the bureaucracy of trying to get the institute to fit some protection (and find the budget to do so) was a problem. The building itself was protected, but the antenna was now the highest point.

So we made up a makeshift LPS using stuff from local hardware shops, in between ice-creams and coffees, and hopefully it will be OK for the future:
View attachment 86202
Nice idea, I'm surprised they wouldn't just stump up for a couple of finials, they tend to be a lot cheaper than the damaged caused by a strike.
 
Nice idea, I'm surprised they wouldn't just stump up for a couple of finials, they tend to be a lot cheaper than the damaged caused by a strike.
Ideally they would have had it done when the building LPS was updated at some point between our original installation and when we had to fix it. We saw the change in conductors, etc, but no thought about a point going above the antenna! There you go :(

Our make-shift one is not ideal, as it would provide weak protection from some directions as not high enough and no time / spare cash to put in a couple of them. But it was the first direct hit in over 20 years so not that common.
 

Reply to SPD in commercial offices in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

We were all told that SPD's were mandatory under A3 from September last year and even sat through the webinar spelling it out. I work an area...
Replies
21
Views
2K
Client needs an SPD fitting but no room in c/u or adjacent. Best bet looks like a parallel connection into the tail blocks in the meter cabinet...
Replies
3
Views
273
Hi all, Grateful for your expertise regarding my confusion on the below. Context: French rural domestic property Single phase supply, TT...
Replies
12
Views
2K
Has anyone fitted an SPD to a schneider standalone AFDD DB. Isobar P B Standalone Active distribution board, Acti9, 24 AFDD ways This board only...
Replies
4
Views
819
Hello, I was looking at installing a SPD into an existing split load RCD BG consumer unit. In the instructions for the SPD it states that it may...
Replies
2
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock