The photo I have taken of a up and coming job shows a wish mash of cables.
The old rewardable board is coming out and the client wants an updated dual RCD board replacing the existing one and the old board.

I don't have a problem with that and have also advised re mains smoke detectors and upgrading of earthing. A few other bits need replacing.

My question relates to the 16mm supply cables. the live appears to be connected at a henly block. The neutral seems to be coming direct from the meter and also direct from the cutout to the split board. I haven't seen this before as I thought everything came from the meter.

To get rid of the old fuse board I will need the supplier to attend and remove the tails that go direct to the meter.

Also the 6mm to the left is nickel plated coper so what is the age of this cable 40 years or so?

Has anyone else seen this set up?
Is the best solution to ask the supplier to just install both tails to henley blocks so i can connect to there.

Thanks in advance.

IMG_0033.jpg
 
The photo I have taken of a up and coming job shows a wish mash of cables.
The old rewardable board is coming out and the client wants an updated dual RCD board replacing the existing one and the old board.

I don't have a problem with that and have also advised re mains smoke detectors and upgrading of earthing. A few other bits need replacing.

My question relates to the 16mm supply cables. the live appears to be connected at a henly block. The neutral seems to be coming direct from the meter and also direct from the cutout to the split board. I haven't seen this before as I thought everything came from the meter.

To get rid of the old fuse board I will need the supplier to attend and remove the tails that go direct to the meter.

Also the 6mm to the left is nickel plated coper so what is the age of this cable 40 years or so?

Has anyone else seen this set up?
Is the best solution to ask the supplier to just install both tails to henley blocks so i can connect to there.

Thanks in advance.

View attachment 40410
The 6mm2 you mentioned will be I imagine an old Imperial cable probably 7/044
 
  • Like
Reactions: Andy C
Looks like whoever installed the later unit was short of a connection block. The choice is yours.
As regards the 6mm, it's tinned copper and probably 1960's, although I don't know which cable you mean on the photo.
Earthing looks dicey ......4 or 6mm?..and I'd check that TN s connection, the cable looks newish.
 
  • Like
Reactions: Andy C
To get rid of the old fuse board I will need the supplier to attend and remove the tails that go direct to the meter.

Not necessary
The neutral from the meter to the old rewireable could be taken out of the fuse board
Lob off (near the cut out) the neutral to the newer board, fit a service connector block,reconnect both neutrals
Put another connector block for the lobbed off neutral thats left poking out of the cut out
 
  • Like
Reactions: Andy C
Think I might get an isolator in there as the work progresses on the cut-out. There is really nothing for the DNO to do. All the wiring there is past the meter so they have no need to touch it at all. Maybe they could remove the neutral for you so you just go into isolator off to your Henley and all else from there.
 
  • Like
Reactions: Andy C
Thought it looked strange, then realised cut-out is upside down, usually have fuse on left. Nothing wrong really, but would be better to have all neutrals to block, just tidier.
 
  • Like
Reactions: Andy C

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Supplier issue? Advice needed please.
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
6

Advert

Thread statistics

Created
Andy C,
Last reply from
Percyprod,
Replies
6
Views
1,846

Advert