Is it ok for you to connect to it ? earth clamp to sheath.

I had a call tonight and a customer could not reset his RCD so no power at all.Ok fixed the fault unlpugged the kettle and it reset as soon as we plug it in it tripped so power all restored.Bid disadvantage of having 1 RCD for whole house.
Double checked earth loop and got over 8.2 ohms on 32amp ring main and thought it could be a loose connection so did cooker socket and got 7.92 for a 40 amp MCB.
Nice bit of 10mm cable on gas and water but no EARTH at meter head,no MET nothing.Had board changed about 10 years ago he said.
All the houses roughly the same in the street all built same time so popped next door and they had a TN-S.Soldered to a wide strip of woven braided steel strap.
So fitted a clamp on cable sheath ,16mm to a MET and 16mm to CU and gas and water connected ,rechecked and got 0.62 ohms on ring so happier now.
I am amazed that it had no earth at all and had been like it for years.It has even had a new digital meter fitted and you would have thought that the meter fitter might have noticed.
No cup of coffee as kettle knackered but £10 tip for coming out.
Should i inform DNO ?
 
Biggest advice I can give to anyone is be persistant with the dno, they kept on giving me different numbers and fobbing me off. In the end when I spoke to a new lady I said "this is a very dangerous situation and needs to be sorted!!!!! oh by the way what is your name?" then to my surprise she said I will put a call out for you ref no......
with in half an hour nice old bloke turns up & bobs your uncle. He did say that they are not obliged to make a connection and could quite rightly charge me for a pme upgrade but as I got a good reading off the sheath he made my day.
I'm now going to earth the metal service head aswell.

Before After
Photo0084.jpg Photo0085.jpg

I learnt a valuable lesson- in my own very house!!! test ze with main earthing conductor disconnected from main earthing terminal before I change a CU. I tested zs at the socket & got a very good reading & thought all was hunky dory when I was only getting a reading through the water and gas pipe.
 
Last edited by a moderator:
Biggest advice I can give to anyone is be persistant with the dno, they kept on giving me different numbers and fobbing me off. In the end when I spoke to a new lady I said "this is a very dangerous situation and needs to be sorted!!!!! oh by the way what is your name?" then to my surprise she said I will put a call out for you ref no......
with in half an hour nice old bloke turns up & bobs your uncle. He did say that they are not obliged to make a connection and could quite rightly charge me for a pme upgrade but as I got a good reading off the sheath he made my day.
I'm now going to earth the metal service head aswell.

Before After
View attachment 5940 View attachment 5939

I learnt a valuable lesson- in my own very house!!! test ze with main earthing conductor disconnected from main earthing terminal before I change a CU. I tested zs at the socket & got a very good reading & thought all was hunky dory when I was only getting a reading through the water and gas pipe.


Just as a matter of interest why is there no supply neutral in the meter above the cut out? Apologies if I've seen it wrong
 
The neutral inside those meters is a solid link - the meter only uses the neutral for measurement of voltage and phase angle. Since the tails go back into the cast iron enclosure, it was probably easier to just take the neutral from the cut-out.
 
  • Like
Reactions: 1 person

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Suppliers Earth TN-S
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
44
Unsolved
--

Advert

Thread statistics

Created
Roger,
Last reply from
pennywise,
Replies
44
Views
7,942

Advert