Remember you are testing the fixed wiring… not the loads on the end, not even a lamp… and you’re not resting the devices in the board either.

So all it is is a bunch of cables. You’re testing there are no shorts where there shouldn’t be, and continuity of cables where there should be.

Which means testing L to E, N to E and L to N…. Last one is where you have to make sure nothing is connected / plugged in.
I feel this comment perhaps give an incomplete picture.

Installed equipment should be tested to ensure that exposed conductive parts are connected to the system earth (typically an R2 test), and that there are no faults between live parts and earth (IR test L+N to earth). Without confirming these, a fault between L and an an un-earthed exposed conductive part could go undetected, leaving a C1 fault.
 
I feel this comment perhaps give an incomplete picture.

Installed equipment should be tested to ensure that exposed conductive parts are connected to the system earth (typically an R2 test), and that there are no faults between live parts and earth (IR test L+N to earth). Without confirming these, a fault between L and an an un-earthed exposed conductive part could go undetected, leaving a C1 fault.
Yes, I did simplify things somewhat… and what I said was really aimed at initial testing, before equipment is connected.

I was also trying to convey the fact that testing N-E was as important as L-E, which was part of the OP query.
 

Reply to Technical question for IR testing in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

Similar Threads

So was on a call out today and cooker circuit kept tripping the RCD. Disconnected at the board and at the cooker switch and IR’d the cable and...
Replies
9
Views
450
Hi, I carry out PAT testing on landlord appliances for letting agents in rented accommodation. Occasionally some of the items I cannot access...
Replies
5
Views
807
In my line of work it's very rare that I ever have to change a DB. I'm largely in maintenance; occasionally have to add new circuits etc. so in...
Replies
3
Views
703
Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Replies
9
Views
660
I have got these questions on 2391-52 inspection and testing but can't remember option of 1st two questions. Please any suggestion will be...
Replies
2
Views
735

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock