Weekend sparker here, I have a sqd 2 pole 50amp GFCI breaker it was mounted out side in a service box, have not had a problem till now 3yrs old, it trips instantly when rest, with the breaker out of the box, I check resistance across the load side of the breaker from either load 1 to neutral or load 2 to N or load 1 to 2 they all start out @ 27ohms and increases to 45+ ohms, if I reset breaker ( it's out of the box) and test resistance from line 1 to load side 2 yes opposite side with breaker on I also have a rising ohm reading 27 and increasing to 39+ohms , I'm coming up with a faulty GFCI breaker that's leaking internally...... Am I on the right path ??? Or do I need to look at spa unit as having a GFCI fault some where
 
If it will energise and stay on when the supply is connected but none of the outgoing cables are connected then the unit is likely ok.
 
Ok. I will try that. I had pulled it to get a better bench test on it when I had seen the raising resistance, and didn't know if it had gotten moisture in it and caused a leak across the the poles or was creating a soft ground point, I never tested a GFCI breaker that had resistance across the load connection's, I was also told sqd breakers are not good for spa units. But at time of install that was all that was available 🤔 so I will try it out in morning..
 
What you see by way of rising resistance on your meter can be caused by eg a capacitor in an electronic circuit charging up (from the battery in your tester), not a fault! The gubbins below require power, so you will see resistance across some terminals from the power supply components.


7AA25C1E-31C8-4ED0-B454-AAD182CAA220.jpeg
 
Ok I see that it could be energizing the trip coil but wouldn't the 2 poles be separated and have there own sensing coil? And then be connected to the neutral line? I could see there being resistance from load 1 to neutral or load 2 but not load 1 to 2.. just a head scratcher gonna be testing in a few when I get home
 
Weekend sparker here, I have a sqd 2 pole 50amp GFCI breaker it was mounted out side in a service box, have not had a problem till now 3yrs old, it trips instantly when rest, with the breaker out of the box, I check resistance across the load side of the breaker from either load 1 to neutral or load 2 to N or load 1 to 2 they all start out @ 27ohms and increases to 45+ ohms, if I reset breaker ( it's out of the box) and test resistance from line 1 to load side 2 yes opposite side with breaker on I also have a rising ohm reading 27 and increasing to 39+ohms , I'm coming up with a faulty GFCI breaker that's leaking internally...... Am I on the right path ??? Or do I need to look at spa unit as having a GFCI fault some where
My suggestion is to replace the 50 amp GFCI breaker. Over time they will go bad.
 

Reply to Testing sqD GFCI breaker in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Having trouble figuring this one out. House was built 5 years ago. Eaton box and breakers. Over the past 3 weeks, the bedroom breaker keeps...
Replies
8
Views
664
Hello, I had an electrician install a 100Amp subpanel which feeds a mini split. I addition I added a Homeline 50A GFCI breaker to power a shed. I...
Replies
9
Views
2K
First, sorry if I'm not in the correxct thread. I'm trying to replace an old switch with a WIFI switch and cannot seem to do it right. There are...
Replies
1
Views
300
So I have a outlet protected by a gfci breaker, and if you use the plug test the gfci doesn't trigger . I replaced the gfci breaker and the...
Replies
0
Views
650
I have a 20 amp gfci pool pump breaker that trips only when the pump is off during the night. Pool pump runs fine all day. I turn pump off...
Replies
2
Views
750

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock