I was sent an EICR to comment on....
When I saw the report :
1. CU not AMD 3 compliant - C3
2. Circuits are not identified at consumer unit - C2 (yet the report lists what they are)
3. Cables buried in walls are not RCD protected - C2
4. Lighting circuit serving bathroom is not RCD protected
Interestingly he commented, but didn't code a slightly high end to end reading on a Ring circuit CPC
Been into the property today, so my thoughts are:
1. No code, CU is in a cupboard off the hall, so not under the stairs or in an escape route
2. No code - but labeling would be sensible
3. C3
4. C2
So the "inspector" has recommended a new CU @£350 + VAT
How can people code in such a way?
I'm investigating if the cu MCB for the lights can be changed for a RCBO (see photo) so if anyone can help me with this I'd be grateful