Discuss TN-S high Ze in the UK Electrical Forum area at ElectriciansForums.net

If you selected a 3 wire configuration for measuring, then it uses a smaller current and is less likely to show-up a problem on a poor joint.

Use the 2 wire measurement as it's more likely to identify the problem!
 
i'd probably tighten clamp bolt and retest.
but i dont expect many to agree with my insane thinking.
;-)
You think that's insane thinking? I was going to suggested smearing the clamp with cold custard (with nutmeg, obviously) and getting on your knees and praying to as many gods as you can think of.
 
agreed...its cheap n slovenly..
theres no reason why a well designed system with a stable, reliable means of earthing cannot meet disconnection times without the magic `RCDs`...it bloody well should be doing anyway...


Thing is I worry as depending on an RCD yet I think we have all had to return 1 or 2 faulty units
 
You think that's insane thinking? I was going to suggested smearing the clamp with cold custard (with nutmeg, obviously) and getting on your knees and praying to as many gods as you can think of.

Cold custard? Don't forget to adjust tabulated max Zs for BS custard by 0.8
 
Thing is I worry as depending on an RCD yet I think we have all had to return 1 or 2 faulty units


I think most here would shudder at the amount of RCDs (of all types) that were returned to manufacturer for replacement on my last and previous projects!! I'm expecting very little change on this project either. And, were talking of a top of the range manufacturer here too!! It's certainly opened my eyes on the reliability of RCD devices!! lol!!
 
1. Check your readings and test equipment are accurate. (You dont want egg on your face)
2. If its higher than 0.8 inform the DNO they have a possible earthing issue.
3. Rcd's are no substitute for a solid low resistance earth return path (End of)

And remember your 1.7 reading is a no load test. It indicates possible failure of the earthing system for reasons not defined. Under fault conditions the current flow could result in all kinds of nasties. Sure 30ma with an rcd on the end but what if ???
 
Call the DNO, wait 45 mins on the phone. DNO will turn up and give you the option of digging up the street or to go PME..
When you choose the PME option (and you will) they will leave and say it needs to be booked in by the meter supplyer as they dont do it themselfs.

make sure gas and water bond is up to size.
Good luck
 
I think most here would shudder at the amount of RCDs (of all types) that were returned to manufacturer for replacement on my last and previous projects!! I'm expecting very little change on this project either. And, were talking of a top of the range manufacturer here too!! It's certainly opened my eyes on the reliability of RCD devices!! lol!!

Youd never guess!!!lol
 

Reply to TN-S high Ze in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Evening Chaps As can be seen in the attached photo , the incoming supply cable has a Earth soldered to the outer sheath of the cable suggesting...
Replies
10
Views
1K
On an EICR I found a 200 amp 3ph supply, TNS earthing (which looks original) and Ze of 19 ohms. No rods. No RCDs. L1 -> N was about 0.5 ohms...
Replies
11
Views
1K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K
Hi, Any suggestions what this black cable is coming off the supply's incoming cable? Its a TN-S system, I thought it could be the earth conductor...
Replies
29
Views
3K
I have come across what I think is a looped supply - like a normal incomer but two of them coming up side by side. It's a TN-S arrangement with an...
Replies
12
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock