New TT supply on unbuilt barn conversion with 8ft of 5/8 rod & reading of 48ohm with current swamp conditions.
next phase is large all wood storage shed with power & lighting fed in 10.0mm 3core ,swa plan is drive another rod & link both or is it possible to export TT earth?
 
Last edited by a moderator:
You can export the earth, have a separate TT island, or link the two.
Safest option would probably be to link the two, with the least safest being to export.
Is there likely to be livestock between the two buildings?
 
You can export the earth, have a separate TT island, or link the two.
Safest option would probably be to link the two, with the least safest being to export.
Is there likely to be livestock between the two buildings?
no livestock so will stick to plan "A" then just curious about the export option.
for safer install the cost of a couple of rods and an inspection manhole ain't huge.
 