Discuss Using pre installed cooker circuit for 13amp or 16amp oven. in the DIY Electrical Advice area at ElectriciansForums.net
Hi again so oven came today it's has a flex cable on it. It's stamped H05VV-F 3G 1.5. so guessing it's a 1.5mm cable. will a 1.5mm cable be ok to be connected to connection plate that is in wall and just changed MCB to 16amp or would I need get electrician to change cable to 2.5mm as well. Cheers
If the oven is supplied with 1.5mm2 cable, then that is fine. If it came without cable, and I was installing it, I'd fit 2.5mm2 by preference, if I thought the terminals would accept it.
Thanks I did look at 1.5mm amp ratings and some said has rating of 15amp is that true? Would it be better to fit 13amp fuse spur switch to protect cooker cable or not?
1.5mm2 cable is within its rating at room temp., but it's likely to be a bit warmer than that behind an oven in an enclosure.
The cable does NOT need protecting against overload, only against short circuit, which the MCB in the CU will do.
Do not run this oven through a 13A fuse for the reasons mentioned earlier in the thread.
Thanks for all your help just wanted double check the 1.5mm would still be in 16amp rating were it's warmer behind the oven in a enclosure then?as only installation instructions I could find were from Curry's and of hisense website and they both said hard wire to 13amp fuse spur. Which seems strange for reasons mentioned here. There were no installation instructions with oven only that it was 3.3kw.
Reply to Using pre installed cooker circuit for 13amp or 16amp oven. in the DIY Electrical Advice area at ElectriciansForums.net
Hi, My current oven is hardwired to a fused connection plate with a 13Amp fuse inside and power switch. That is then connected to the MCB labelled...
Hi, I'm installing a Hoover oven and would like a little help please. The oven code is HOC3158IN. The oven manual states "The power cable must...
The electrician that installed my cooker circuit put in 10mm cable with a 32a fuse, a 45a cooker switch and 10mm cable to the backplate for behind...
Good evening, I am new to the forum, and I am after some advice I am looking at buying my son a new oven, but have just noticed that the one I...
Here is my situation We have a dedicated oven circuit in our house with a 40A RCBO We have bought a dual fuel range cooker which states it has a...