Where do people record the Ze & PFC of a 3 phase installation, if there is say 10m of 25mm tails between the 4 pole isolator (next to the meter) and the 3 phase distribution board, therefore some (though negligible) resistance?

Do you tend to test at the origin, and record that result, or do you regard the MET as being at the DB (as an extension of what is at the meter position) and do your tests there?

Or both, but only use the one at the origin as a reference, and not record it?

Interested to see what people make of this!
 
I'd say ideally it should be recorded right at the origin of the supply in the building as there's a separate part on Schedules of test results for 'zDB'.
But if there isn't a main isolator at the intake it wouldn't be practical with no access to line conductors without removing a DNO fuse...
On an installation where the DNO fuse, meter and CU are right next to each other I'll generally just do the Ze at the CU main switch incoming terminals, with all main bonding conductors disconnected.
 
I always do it at the bottom of the main switch of the DB, technically that's where the "installation" starts, as any other DB would require another cert. Record the highest reading achieved out of 3 phases (should be the same or very close to each other, same as the PFC).
 
If it's not convenient to switch off the supply so you can disconnect the earthing conductor in order to measure the Ze at the origin, then you cannot measure the Ze at all. You can determine the declared Ze from the DNO, and you can measure the Zs at the DB.
 
If it's not convenient to switch off the supply so you can disconnect the earthing conductor in order to measure the Ze at the origin, then you cannot measure the Ze at all. You can determine the declared Ze from the DNO, and you can measure the Zs at the DB.
Quite a common practice, especially in the office blocks where one of the breakers i marked up "server room" 👍
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Manchester
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Where to measure Ze, opinions welcome!
Prefix
UK 
Forum
UK Electrical Forum
Start date
Last reply date
Replies
7
Unsolved
--

Advert

Thread statistics

Created
LR1397,
Last reply from
nicebutdim,
Replies
7
Views
2,424

Advert

Back
Top