Discuss Wierd one in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
C
Cirrus
Installed 2 new ccts in a house today. Did all dead tests and results were good. Ze was 0.30 ohms on a TT system with 6mm down to spike. Powered up and then did Zs and came out at 0.34 Kilo Ohms on all ccts:eek:
How can this be?????
firstly i think you mean Zs (with bonding attached) .30 is very very low for a Ze on a t,t
as for Zs being that high i can only think a loose conection,what are the earth loops at the first piont on each circuit if thay are as high the problem is in the board ie loose earth bar what pfc reading do you get L-N
if it is olso high it point to a loose line conductor
Sorry - pfc was .030 ohms. Can't be a loose connection as it is over 3 ccts that I tested (maybe more) and 2 were installed by me. I do 15 of these a month and never have issues so I know it ain't a loose connection in either my final ring circuit or cooker circuit.
PFC measured in ohms?
I have had low Ze readings for the last few TT systems I have had. This was a 6mm earth and the spike was 7 feet from the baord.
The only time i have had very low (i mean very very low)readings on my Ze was when the customer had a sub station at the bottom of his garden,dont know why but there you go.i think you need the welsh wizard to unravvle this mystery scooby.
Reply to Wierd one in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Hi, I did my first EICR on a TT system today and the Zs was a lot higher than Ze+R1+R2 on everything. Zs was around 3.5 ohms on all of the ring...
OLDBOY
O
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...