Reaction score
229
As some of you know, I'm doing a first fix for family member. I now know that in a modern house its best to do loop method of wiring from switch to switch due to modern day down lighters and light fittings only accepting one cable. I did have a thought though (bear with me) as there are 3 x cupboards on the ground floor of using flush joint boxes in each one to wire the various light switches to etc. I would still loop each LED down lighter together though. so all j/boxes would be accessible for test inspection and maintenance. Anyone done similar? thanks
 
Yes, I much prefer wiring lighting using the central joint box method and have put them in cupboards before if there is space and it will be possible for anyone to find it again in the future.
 
Yes, I much prefer wiring lighting using the central joint box method and have put them in cupboards before if there is space and it will be possible for anyone to find it again in the future.

Great, I was expecting to put my battered tin hat on again! what type, manufacture do you use? Is there a standard product out there? Possible din -rail connection, wagos?. I've only used J701 I think they were called. Thanks
 
I very rarely use 3 plate to the rose, pain in the backside for 2nd fixing and for customers who like changing their own fittings

I tend to wire to the switchs or of late i have been wiring a central joint box which consists of a large plastic adaptable box , series of stuffing glands drilled in, all cables labelled and connected accordingly and then positioned in a place which is accessible
 
the good old spider wiring, brought from the 60's into the 21st century.
 
As some of you know, I'm doing a first fix for family member. I now know that in a modern house its best to do loop method of wiring from switch to switch due to modern day down lighters and light fittings only accepting one cable. I did have a thought though (bear with me) as there are 3 x cupboards on the ground floor of using flush joint boxes in each one to wire the various light switches to etc. I would still loop each LED down lighter together though. so all j/boxes would be accessible for test inspection and maintenance. Anyone done similar? thanks

No problems with that at all, i would still loop out at the switches myself but nothing electrically wrong with your method at all !!
 
3 plate without doubt is a good tried and trusted method, however these days with LED downlights and posh chandaliers wiring through the switches is prefered by a lot of sparks so there is only a pair at the light, I understand that and agree it is a good method, I personally wouldn't create more joints by adding an adaptable box in a cupboard to be the connection unit but it is installed a fair bit these days and again nothing wrong with it, just not my cup of tea.
 
Before you all go overboard have a look for the “octopus” wiring system. It’s been around for years. Great for testing and fault finding so long as the central box is accessible.
 
J701 does fine for me.

I was thinking something on the lines of being flush as opposed to surface box like J701. What about if say an Appleby 665 double metal flush box with a blank plate was used. I've never used Wagos before but could those as opposed to choc - blocks which I would of used years ago.
 
3 plate without doubt is a good tried and trusted method, however these days with LED downlights and posh chandaliers wiring through the switches is prefered by a lot of sparks so there is only a pair at the light, I understand that and agree it is a good method, I personally wouldn't create more joints by adding an adaptable box in a cupboard to be the connection unit but it is installed a fair bit these days and again nothing wrong with it, just not my cup of tea.
usually we do 3plate but we do it with a jb next to downlight, can remove downlight to easily gain access if you need to.
 
usually we do 3plate but we do it with a jb next to downlight, can remove downlight to easily gain access if you need to.
Thats okay if you have a small 20 amp lighting JB, if 1mm2 is used and the downlight hole big enough to get the JB out if required, nothing wrong with it though of course.
 
Thats okay if you have a small 20 amp lighting JB, if 1mm2 is used and the downlight hole big enough to get the JB out if required, nothing wrong with it though of course.

Re J/B's in roof space. Should not all J/B's be firmly fixed as opposed to floating? Even if 17th edition whereby cables are clamped entering the J/B's.
 
3 plate without doubt is a good tried and trusted method, however these days with LED downlights and posh chandaliers wiring through the switches is prefered by a lot of sparks so there is only a pair at the light, I understand that and agree it is a good method, I personally wouldn't create more joints by adding an adaptable box in a cupboard to be the connection unit but it is installed a fair bit these days and again nothing wrong with it, just not my pint of Creamflow.


Fixed that for you Mark.

There will be no charge. :)
 
I've never used the central JB method for light circuits, but i'd rather use that method than looping through switches, which is something i've never done and never will. Nothing against neutrals in switch boxes, but only when and if they are needed, and 9 X out of 10, they never will be in a domestic installation.
 
I've never used the central JB method for light circuits, but i'd rather use that method than looping through switches, which is something i've never done and never will. Nothing against neutrals in switch boxes, but only when and if they are needed, and 9 X out of 10, they never will be in a domestic installation.

This is an odd occasion when I'm inclined to disagree with you matey. More and more houses are now wanting things like one-touch / remote dimmers, receivers for home automation etc etc, and whilst yes I'd agree that this is a percentage far less than 50%, I'd say it's rapidly developing into far more than your 10%, and growing - especially on higher spec new builds. Having given the matter some thought, whilst I'm not going to stray from loop at ceiling unless there's a good reason (let's face it, there are times when loop at switch DOES make sense) I think I will start using 3c as switch drops instead of 2c on new builds - it's a handful of pence on a domestic job - just to future proof.
 
This is an odd occasion when I'm inclined to disagree with you matey. More and more houses are now wanting things like one-touch / remote dimmers, receivers for home automation etc etc, and whilst yes I'd agree that this is a percentage far less than 50%, I'd say it's rapidly developing into far more than your 10%, and growing - especially on higher spec new builds. Having given the matter some thought, whilst I'm not going to stray from loop at ceiling unless there's a good reason (let's face it, there are times when loop at switch DOES make sense) I think I will start using 3c as switch drops instead of 2c on new builds - it's a handful of pence on a domestic job - just to future proof.

As i say if a neutral at a switch is needed FINE, i have no objection whatsoever. As for looping through the switches, no way will i ever go down that route!! It's also a fallacy that less wiring is needed, you'll be using more cable, every switch drop will require a minimum of two cables. I've seen what happens when you have combinations of 2 way switching and/or intermediates at switch positions, ....a total mess of crammed in cables, filling even 45mm back boxes!! No thanks!! lol!!
 
I've never used the central JB method for light circuits, but i'd rather use that method than looping through switches, which is something i've never done and never will. Nothing against neutrals in switch boxes, but only when and if they are needed, and 9 X out of 10, they never will be in a domestic installation.

You obviously don't keep up to date with modern devices and trends eng! Plenty of people now wanting more high tech stuff than just a single pole light switch :) Daz
 
You obviously don't keep up to date with modern devices and trends eng! Plenty of people now wanting more high tech stuff than just a single pole light switch :) Daz

Working on the bigger projects, i'm probably more upto date with modern devices than most. But i'd still feel confident saying that the vast majority of British homeowners that purchase new builds or want/need a rewire to their property won't be thinking of any of the fancy gizmos you have in mind, and certainly not at every light switch in the house.... Trends take a long time to materialise in the UK and forgotten about a damn sight quicker...lol!!
 
Working on the bigger projects, i'm probably more upto date with modern devices than most. But i'd still feel confident saying that the vast majority of British homeowners that purchase new builds or want/need a rewire to their property won't be thinking of any of the fancy gizmos you have in mind, and certainly not at every light switch in the house.... Trends take a long time to materialise in the UK and forgotten about a damn sight quicker...lol!!

I agree, it's early days yes. But it's the way things are going like it or not. Daz
 
i prefer line products kit. much quicker and a bit cheaper also.
 
Working on the bigger projects, i'm probably more upto date with modern devices than most. But i'd still feel confident saying that the vast majority of British homeowners that purchase new builds or want/need a rewire to their property won't be thinking of any of the fancy gizmos you have in mind, and certainly not at every light switch in the house.... Trends take a long time to materialise in the UK and forgotten about a damn sight quicker...lol!!

Agreed that it takes time to move a mountain (so to speak) but I think you'd find the front counters of a wholesalers an eye opener!
 
Yes , thats why I'm asking. I would of thought this day and age floating j/boxes were a thing of the past. i can see that i'm wrong though. Hence electricians designing the installation to suit. ie loop in via switches.

These have cable clamps - buy a couple and try them, they are ideal in certain situations
 
The regs say (correct me if I'm wrong) that floating junction boxes need to have strain relief at the cable entry points. Daz
 
The regs say (correct me if I'm wrong) that floating junction boxes need to have strain relief at the cable entry points. Daz
Ok understand......So when doing recessed LEDs say with 2 x cables at each fitting, are fittings designed to terminate both cables direct or best via j/box at each and every fitting?
 
The regs say (correct me if I'm wrong) that floating junction boxes need to have strain relief at the cable entry points. Daz

That is one that doesn't make sense to me. You would have thought it more likely for a fixed JB to need strain relief if cables pulled?
 
That is one that doesn't make sense to me. You would have thought it more likely for a fixed JB to need strain relief if cables pulled?

Eh? If the junction box is loose and floating then it can move about, thus loosening cables. Think about it!! Daz
 
Eh? If the junction box is loose and floating then it can move about, thus loosening cables. Think about it!! Daz

Just my opinion as to a flaw in regs in that unless a fixed JB has cables clipped (easily pulled out) to entry points, the strain relief is more important. Also, it's always fixed JB's that get damaged/lids broke off.
 
Just my opinion as to a flaw in regs in that unless a fixed JB has cables clipped (easily pulled out) to entry points, the strain relief is more important. Also, it's always fixed JB's that get damaged/lids broke off.

It's not a flaw in the regs though - they say that fixed wiring should be just that - fixed! Daz
 
It's not a flaw in the regs though - they say that fixed wiring should be just that - fixed! Daz

I see your point Daz, movement, metal fatigue, movement loosening connections etc., it's just my view and as said in another post, D/L connectors are provided. Some have no strain relief but are far more likely to suffer 'movement'
 

Reply to wiring downstairs light circuits in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
802
Strange on this, we are wiring an extension at the moment and I would like to 3 way the (currently 2 way) landing switch to the new bedroom so...
Replies
14
Views
697
First, sorry if I'm not in the correxct thread. I'm trying to replace an old switch with a WIFI switch and cannot seem to do it right. There are...
Replies
1
Views
361
Good Morning need some advice please. Yesterday went to change a light fitting in hallway. There are two ceiling lights in the hall controlled by...
Replies
6
Views
282
Hi everyone I've moved into a flat and I've decided to replace the original electric switches and sockets with white ones. I've done them all...
Replies
3
Views
921

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock