Hi Guys
Doing an EICR of a property.
The client has an outbuilding with gas and water supplies. It has it's own CU fed from the main CU in the house.
The water is bonded but the gas is not.
The water supply is underground from the house in plastic and then changes to copper which is bonded.

The gas supply comes from the house in an underground copper pipe linked to the gas pipes in the house. So, electrically, it would be subject to the bonding in the house.
But does this negate the need to bond it in the outbuilding?

Looking forward to wise words!

Cheers
Pete:confused:
 
Last edited by a moderator:
NO, it doesn't negate main bonding to the outbuildings CU (EMT) especially if the supply is PME, in which case the sub-main earth should be a minimum of 10mm....
 
NO, it doesn't negate main bonding to the outbuildings CU (EMT) especially if the supply is PME, in which case the sub-main earth should be a minimum of 10mm....

I read it that he is saying the gas is bonded in the house and is in copper pipe to outbuilding so is bonded already. The Water they have bonded in outbuilding because it has plastic pipework across to it.
 
I read it that he is saying the gas is bonded in the house and is in copper pipe to outbuilding so is bonded already. The Water they have bonded in outbuilding because it has plastic pipework across to it.

It doesn't matter a jot whether the gas pipe is bonded at the main house or not, it still needs bonding at the outbuilding....
 
I read it that he is saying the gas is bonded in the house and is in copper pipe to outbuilding so is bonded already. The Water they have bonded in outbuilding because it has plastic pipework across to it.

Yes. your interpretation is correct.
My immediate thought was that it should be bonded, but I couldn't understand why it hadn't been done as the gas supply is an easy connection within 2 metres of the CU and all services were put in at the same time, 10 years ago. The water stopcock and bonding point are miles away.
Pete
 
So with no more information than a blue plastic pipe entering a building and then converting to copper you have decided it does not need bonding? Without any information as to where that copper goes or how it is installed which could make it extraneous?
You need to google the definition of extraneous.
 
Im not talking about the plastic pipe. I am talking about the copper installation in the outbuilding. You do not know that it is not extraneous without testing it first.
 
Im not talking about the plastic pipe. I am talking about the copper installation in the outbuilding. You do not know that it is not extraneous without testing it first.

Indeed. But if testing shows it to be extraneous, the problem may be working out WHY it's extraneous and therefore WHERE it should be bonded.
 
Well when I went to school plastic did not make a good material for conducting electricity.

Read post #26!! I know the plastic pipe is not conductive ffs. I am talking with regard to the copper installation in the outbuilding. We know nothing about it from the OP's opening post so you cannot possibly know if it is extraneous or not as you don't have enough information to make that judgement.
 
Last edited by a moderator:
Again, the definition of extraneous needs to be googled.

I know what an extraneous conductive part is and what defines it (Extraneous-conductive-part: A conductive part liable to introduce a potential, generally earth potential, and not forming part of the electrical installation). How do you know it is not from the limited information the OP has provided regarding the copper installation pipework?
 
NO the incoming pipe is plastic.

Yes the incoming pipe is plastic, but the installation it feeds is copper. There is no information as to how extensive the copper installation is or whether it is all surface pipework on plastic clips or mostly buried in the concrete floor structure or it could even go back underground as copper to feed another building.

Without further information there is no way to know whether or not the installation pipework will be an extraneous conductive part.
 
Yes the incoming pipe is plastic, but the installation it feeds is copper. There is no information as to how extensive the copper installation is or whether it is all surface pipework on plastic clips or mostly buried in the concrete floor structure or it could even go back underground as copper to feed another building.

Without further information there is no way to know whether or not the installation pipework will be an extraneous conductive part.

544.1.2 says "The main protective bonding connection to any gas, water or other service shall be made as near as practicable to the point of entry of that service into the premises."

Since it refers to the point of entry of the service, rather than the point of entry of the pipework, it appears to be saying that, even if the reason that the copper pipework is extraneous is that it feeds out underground in copper, the main bond should still be made at the incoming point.
 
Yes the incoming pipe is plastic, but the installation it feeds is copper. There is no information as to how extensive the copper installation is or whether it is all surface pipework on plastic clips or mostly buried in the concrete floor structure or it could even go back underground as copper to feed another building.

Without further information there is no way to know whether or not the installation pipework will be an extraneous conductive part.

So the incoming pipe is plastic with a bond on it that's not needed. Ok we got there.
Yes it could go underground again (like the gas has and we said move the bond over to that pipe), and if it was copper then it would be bonded at that point would it not.
Am I right in thinking if a house had plastic gas & water incoming pipes and copper installation pipes that did not go underground again, you would bond the pipe work?
TJ, I think your comment of the word "Stupid" over steps the mark!!
 
544.1.2 says "The main protective bonding connection to any gas, water or other service shall be made as near as practicable to the point of entry of that service into the premises."

Since it refers to the point of entry of the service, rather than the point of entry of the pipework, it appears to be saying that, even if the reason that the copper pipework is extraneous is that it feeds out underground in copper, the main bond should still be made at the incoming point.

Which supports my point exactly.

Although you would have to check exactly what they mean when they say 'service' and how you apply it. I would say in the situation that it is not the incoming service which is being bonded but the installation pipework and as such would be best to be bonded at the point that the extraneous part enters the installation.
 
?
Yes. your interpretation is correct.
My immediate thought was that it should be bonded, but I couldn't understand why it hadn't been done as the gas supply is an easy connection within 2 metres of the CU and all services were put in at the same time, 10 years ago. The water stopcock and bonding point are miles away.
Pete


Did it comply then?
 
Which supports my point exactly.

Although you would have to check exactly what they mean when they say 'service' and how you apply it. I would say in the situation that it is not the incoming service which is being bonded but the installation pipework and as such would be best to be bonded at the point that the extraneous part enters the installation.

I agree. It would be better to bond at the point where the metallic pipework enters the building, which isn't what the regs appear to be saying.
 
544.1.2 says "The main protective bonding connection to any gas, water or other service shall be made as near as practicable to the point of entry of that service into the premises."

Since it refers to the point of entry of the service, rather than the point of entry of the pipework, it appears to be saying that, even if the reason that the copper pipework is extraneous is that it feeds out underground in copper, the main bond should still be made at the incoming point.
wrong.

then a block of flats only has bonding on the intake into the building and nothing in the flats?

each seperate building requires bonding in this case the house and outbuilding both need bonding
 
wrong.

then a block of flats only has bonding on the intake into the building and nothing in the flats?

each seperate building requires bonding in this case the house and outbuilding both need bonding

You misunderstand my point.

The regs seem to be saying that extraneous pipework have to be bonded where the supply (water/gas) enters, rather than at the point that makes the pipework extraneous, which could be where another building or an outside tap is supplied.
 
You misunderstand my point.

The regs seem to be saying that extraneous pipework have to be bonded where the supply (water/gas) enters, rather than at the point that makes the pipework extraneous, which could be where another building or an outside tap is supplied.

You need to drop the supply part, it could be uni-strut with tray that enters the building from outside in contact with ground. Supply service is just an example.
 
You need to drop the supply part, it could be uni-strut with tray that enters the building from outside in contact with ground. Supply service is just an example.

I agree that main bonding may be required to extraneous parts other than services. However, where it is a service, 544.1.2 defines where the bonding connection should be made, namely where the service enters the premises.
 
I agree that main bonding may be required to extraneous parts other than services. However, where it is a service, 544.1.2 defines where the bonding connection should be made, namely where the service enters the premises.

Neither the gas nor the water in the outbuilding in the OP is entering the premises though, yet one certainly needs bonding and the other might.
 

Reply to Bonding Gas Supply in an Outbuilding in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Greetings, I am homeowner and looking to confirm if I will need earth boding to water pipes. There is already earth boding near Gas meter and the...
Replies
23
Views
938
I know once you see plastic entering then you don’t need to bond as it says on site guide.(enters the house plastic then it’s metal) Would I be...
Replies
14
Views
2K
Not sure on this one. Mains water is coming up from the ground in lead pipe in bathroom. 2 inches of copper pipe before the stop tap. All...
Replies
4
Views
1K
Hello, Carrying out remedial work on a commercial site and I've come across a metal out building that has a water supply to it. The water pipe...
Replies
6
Views
1K
Hi, went to have a look at a job today, customer has had gas supply company out (for another issue) and they have commented that the protective...
Replies
1
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock