I see that some relays the start and reset are the same input.
You mean some safety relays? The start/reset commend to them can be the same, they can't re-start a machine on their own, they are not allowed to.
Could you have a key and reset button latching a relay with contacts in series with a start button to take care of the deliberate action?
Not sure what you mean. You would have to have a key to comply with BS4163, this could be reset of the e-stop, or start, and the other action could, be a push button. Probably thinking about this in EN 13849 language the reset should be a blue pb, with the re-energise being the momentary key operation.
So if a Emg stop Is pushed to restart you have to twist the key and push reset to acknowledge activation then push start?
This depends on the design, blue is required as the reset under EN 60204-1 which is also called by BS 4163. So blue to reset, momentary, resets the safety relay, to allow re-energising the supply system, then momentary operation of the key switch to re-energise the supply.
I presume all the Emg stops are wired in two loops when it's dual channel, the stop at the key station would be wired like a Emg stop but just a flush red button?
Allowing for the effects of fault masking then yes. the stops would all be wired in series. However, this depends on the analysis under EN 13849 as to what the requirements for the mitigation of fault masking are. There are basically two channels in series in parallel, yes.
The stop at the single start location could be just a red button, but it could not be flush it must be proud. However, if it has the same action as the emergency stop buttons, then it must be an emergency stop button. If you implement a normal stop action at the start location, then you would also have to provide an emergency stop at the location in the event that the stop did not function, the normal stop could bypass the safety relays, but, if it had any influence on the safety circuit/function then it would fall under the same requirements.