Hi,
1. Why did you open the head? You have no right to do so and the older ones can and do go bang. (research arc flash).
2. When you did the the PEFC test did you isolate the installation, disconnect the earth cable from the terminal shown and test at that terminal?
1. I did not open the head - I was not the photographer.
2. Yes I did. To avoid any chance of multiple earth paths.
I would go for TN-C-S.
If you look carefully at incoming supply, the concentric cable has only 2 conductors. The centre line conductor and outer stranded neutral. Part of the stranded neutral has been seperated and used to feed the earth terminal. (Effectively creating a link between them) the remaining strands have then been painted black to form the neutral conductor.
So to my eyesight, which is not what it was, it's combined in the service head, therefore TN-C-S.
Reactions: Rpa07
The neutral and cpc are not combined in the service head and are separate split like the picture
Never seen cable like that Ian.
Having had another look I think your right.
Reactions: Rpa07
The picture from the OP really couldn't make it any more obvious.
Reactions: Risteard
Thanks for the picture - that looks very much like the configuration in the image I originally posted. Just to clarify is the consensus still that this is TN-S?
This would align with the observation that the PEFC and PSSC are different.
Thanks again for very helpful insights from the forum.
Time to go to spec savers I think, there are clearly three separate conductors there!
jlrb,
Lee42,