Quality pull switch or cheap one, they are not as easy to replace as many think with 6 or 10mm cables. If the OP has changed a number of switches I'd suggest the terminations are loose/poor. I've seen plenty of cheap'uns go on for years if connected by someone who knows what they are doing.
 
don't know why people insist on using the pull cord to turn an electric shower on/off,when the shower has a perfectly good (and more functional) on/off switch itself

main reason is that the on/off switch on the shower can only be reached when you are standing in the shower. then you get a deluge of freezing cold water on your head till the pathetic over rated kettle element in the shower manages to warm the water up.
 
32a breaker however so no problem ther3
 
With the OPs Scenario I'd limit the shower rating to 8.5kW max, especially if there are kids about who don't know the meaning of a quick shower.
 
  • Agree
Reactions: Deleted account
32a breaker however so no problem ther3
It is a problem as a protective device is not to be used as a current-limiting device. It is incorrectly selected for the load.
 
It is a problem as a protective device is not to be used as a current-limiting device. It is incorrectly selected for the load.

Had a colleague once who had the shower at home on a B20 to stop the kids being in there too long ! :)
 
  • Agree
Reactions: Dave OCD
Same bloke was on Economy 7 and he and his missus would fill 2 flasks very early each morning using the cheap rate then use the flasks all day for tea making, true I swear ! :)
 
main reason is that the on/off switch on the shower can only be reached when you are standing in the shower. then you get a deluge of freezing cold water on your head till the pathetic over rated kettle element in the shower manages to warm the water up.

Northern softy, thought you lot were made of sterner stuff ;)
 
I agree with Midwest,its an isolator not a light switch
3 pull cords in a year seems to be the penalty your paying for using the shower isolator like a light switch

Get a 50 amp Crabtree pull cord, leave the thing in the on position,it may even outlive the shower unit and it will also be immune to being used by Scousers
 
  • Winner
Reactions: Rpa07
Sorry, got myself confused trying to give as much information.
My question is:
Do the values seem ok for the cable size?
No, you have 9.5kw shower which is 41.3A total load
you need minumum 10mm twin and earth cable
5oA pull cord shower switch
45A MCB
rather safe than sorry
 
No, you have 9.5kw shower which is 41.3A total load
you need minumum 10mm twin and earth cable
5oA pull cord shower switch
45A MCB
rather safe than sorry
BOLLOX. 9.5kW = 39.6A . 6mm clipped direct on a 40A or 45A MCB.
 
  • Agree
Reactions: Des 56 and Pete999
Northern softy, thought you lot were made of sterner stuff ;)
in actuality, we don't have an indoor shower. ours is a hosepipe and a colander in the back yard.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Cable size issue with size of shower
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
49

Advert

Thread statistics

Created
Linksy5,
Last reply from
Deleted member 9648,
Replies
49
Views
5,714

Advert