So why is this done out there, having main switch on the board rated higher than the fise in the head, it dont make sense the fuse in the head would alway blow first.
Do you not think it a good idea to have a switch rated equal or higher to the current that could be drawn through it?
What Reg are you referring to?
Under the Electricity safety, quality and continuity regulations 2002 you cannot use a suppliers earth to an out building, on a TNC-S Earthing arrangement, so the detached garage effectively becomes a TT installation with an earth electrode installed in the ground.
Ok lets say you exported the earth on a tncs to an outbuilding, and then lets say you lost your neutral at the main incoming, if you had a live to earth or neutral short, every thing connected to earth would become live under fault conditions, hence why you need to rod and not export form the main earth to exterior building ect
There are a couple of reasons why you would not export a PME earth.
One could be if the exterior of the outbuilding is metal, and the other is if there are extraneous conductive-parts which would require bonding.
At the end of the day, it boils down to cost.
Is it cheaper to run a 3 core 10mm2 armour or a 2 core armour and install an earth rod.
So why is it matter if it is an outbuilding or not? That would still happen in a building that is not an outbuilding.
….deleted
A common mistake, you are so unfamiliar with seeing TN-C you brain reads TN-C-S.
Reactions: Michael J
TN-C-S is where the DNO supply is TN-C but is presented to the customer as TN-S.
What?
A TN-C-S is where the earth is taken from the PEN within the installation.
A TN-C is where the same connection is made outside of the installation.
A TN-C system has a combined neutral/earth on the service side and throughout the consumers installation, very unusual.
Cable calculation
Commercial Electrical Advice
Simon Burton,
ackbarthestar,