Sep 13, 2016
594
53
1,203
London
Hi, have a distribution unit which feeds some caravan boxes TT system, it has upfront 300mA RCD and double pole 60898, now I’ve been sent to re gland as the disconnect times wasn’t met, but I’m getting readings of 0.30 ohms when max is either TT 167 ohms or if you go by MCB then 0.59? But the boxes have there own RCD/MCB Maybe last persons tester wasn’t calibrated? Very low but paralel paths?
Where in the site are you getting readings of 0.3 Ohms?
The panel which feeds the panel I’m getting 3.15 ohms and the 1st panel is 4 meters from ground mounted transformer
So Ze on panel next to transformer is 0.3 and this goes 30/40 meters to panel I’m getting 3.15 ohms
Assuming this is the 400A 60947-2 device you mention in your other thread the 0.30 Ze at source is too high without needing to know the Zs. Aside from needing to know the manufacturer and other details it will be too high.
Reactions: Wilko
I’m thinking tighten up the gland and see what I get and yes it’s 4 core 120mm
Cant you test the swa braiding with shroud removed? This will eliminate the gland being the problem if still high reading.
I would not be happy having the site on TNS as there is no way of guaranting the supply its pme at transformer or may be in the future. TT it.
London
Caravan site readings on TT system
Bradley6969,
bigspark17,