Discuss Caravan site readings on TT system in the UK Electrical Forum area at ElectriciansForums.net
Hi, have a distribution unit which feeds some caravan boxes TT system, it has upfront 300mA RCD and double pole 60898, now I’ve been sent to re gland as the disconnect times wasn’t met, but I’m getting readings of 0.30 ohms when max is either TT 167 ohms or if you go by MCB then 0.59? But the boxes have there own RCD/MCB Maybe last persons tester wasn’t calibrated? Very low but paralel paths?
Assuming this is the 400A 60947-2 device you mention in your other thread the 0.30 Ze at source is too high without needing to know the Zs. Aside from needing to know the manufacturer and other details it will be too high.
I’m thinking tighten up the gland and see what I get and yes it’s 4 core 120mm
Cant you test the swa braiding with shroud removed? This will eliminate the gland being the problem if still high reading.
I would not be happy having the site on TNS as there is no way of guaranting the supply its pme at transformer or may be in the future. TT it.
Reply to Caravan site readings on TT system in the UK Electrical Forum area at ElectriciansForums.net
There’s been a few recent threads about caravans, caravan sites etc, and I thought I’d post up some photos I took today while on one such site...
Good Morning everyone. Quick question regarding a sub main from a TNCS supply feeding an outbuilding on TT. This is a domestic installation not...
  • Locked
I've been testing a static caravan installation. At the plastic meter box outside the 'van (which contains an RCD, 16A MCB, meter and 16A socket...
I'm doing an EICR on a static caravan after being called on to fix to a couple of problems due to loose connections. It's all fine now within...
6K
Hi guys, New job looking at. I haven’t been to site yet, but this is the scenario. DNO just put a new single phase supply into a field PME...