If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)
Hi, have a distribution unit which feeds some caravan boxes TT system, it has upfront 300mA RCD and double pole 60898, now I’ve been sent to re gland as the disconnect times wasn’t met, but I’m getting readings of 0.30 ohms when max is either TT 167 ohms or if you go by MCB then 0.59? But the boxes have there own RCD/MCB Maybe last persons tester wasn’t calibrated? Very low but paralel paths?
 
Where in the site are you getting readings of 0.3 Ohms?
The panel which feeds the panel I’m getting 3.15 ohms and the 1st panel is 4 meters from ground mounted transformer
 
So Ze on panel next to transformer is 0.3 and this goes 30/40 meters to panel I’m getting 3.15 ohms
 
Assuming this is the 400A 60947-2 device you mention in your other thread the 0.30 Ze at source is too high without needing to know the Zs. Aside from needing to know the manufacturer and other details it will be too high.
 
  • Agree
Reactions: Wilko
I’m thinking tighten up the gland and see what I get and yes it’s 4 core 120mm

Cant you test the swa braiding with shroud removed? This will eliminate the gland being the problem if still high reading.
I would not be happy having the site on TNS as there is no way of guaranting the supply its pme at transformer or may be in the future. TT it.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
London
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Caravan site readings on TT system
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
12

Advert

Thread statistics

Created
Bradley6969,
Last reply from
bigspark17,
Replies
12
Views
2,806

Advert