Not changed any glands yet and only going by EICR at the moment, so I’m getting 1.13 ohms on earth loop but if I go to PSC L+N is 0.26 so may get round it that way as will still disconnect in required time, have 63amp 60898 MCB at mains DU then feed the caravan boxes
 
It would be good if the OP could clarify the test results and what they mean by original values. Their other threads recently about this same job make me think these original values refer to the EICR conducted before they started the remedials rather than referring to an EIC.
Yes sorry
 
TNS system
60947-2 main switch
60898 double pole 63amp MCBs that feed some caravan boxes now some circuits I can get below the disconnection times of 0.56 ohms but some are 1.22 ohms now I’ve tried changing glands anything else I can do apart from TT the hook up unit? Or do you need upfront RCD

If not change the distribution unit feeding boxes with RCD and Rod it

Not changed any glands yet and only going by EICR at the moment, so I’m getting 1.13 ohms on earth loop but if I go to PSC L+N is 0.26 so may get round it that way as will still disconnect in required time, have 63amp 60898 MCB at mains DU then feed the caravan boxes

You're contradicting yourself.

PSC L+N is 0.26 so may get round it that way as will still disconnect in required time

What do you mean by this then?
 
  • Like
Reactions: DPG
You're contradicting yourself.



What do you mean by this then?
Sorry meant to put I’ve not tried changing any glands yet

Well calculates the max current flow between L+N same as earth loop between L+E in the event of a fault?
 
So you’ve taken pscc at the origin and your testers also give you a Ze reading but that would include any parallel paths as well? I’m so confused.....did you take Ze with main earth disconnected?
I’d go with Petes post a while back and get some R1-R2 readings from the swa....
 
Ok, but what has that got to do with Zs requirements?
Well you do a Zs at a panel/consumer so PSCC and PFC and record highest what’s difference but just another sub circuit? As if you measure either of these on my tester you get impedance value and kA so breaking capacity?
 
Again, what has PSCC and PFC got to do with the Zs requirements?

Either I am misunderstanding the point you are trying to make, or you don't fully understand the difference in tests and what to do with the results.
 
  • Agree
Reactions: ChipFanDave
In order to get the values write in the being at the incoming what was the ohms and the ka.
Ovasly you have sub circuits to diffrant pitches ,the sub circuits are on bs60898 and you are testing each circuit ,but some how you are getting well beyond the max range .
Are the glands in good order or they
Are not earthed correctly.some how we are going round the caravan pictches if you know what i mean.
 
In order to get the values write in the being at the incoming what was the ohms and the ka.
Ovasly you have sub circuits to diffrant pitches ,the sub circuits are on bs60898 and you are testing each circuit ,but some how you are getting well beyond the max range .
Are the glands in good order or they
Are not earthed correctly.some how we are going round the caravan pictches if you know what i mean.
Well the panel feeding the sub circuits has Zs of 3.15 and KA of 3.0 but some of the circuits are ok and some are not but there are endless joints underneath the ground so can’t help and glands are ok
 
So the Zs of the sub circuit is 1.22 ohm, the Zs at the panel feeding these is 3.15 ohm?
 
So the Zs of the sub circuit is 1.22 ohm, the Zs at the panel feeding these is 3.15 ohm?
Yes, at a guess paralel paths
 
you need to make proper arrangements with the client so you can turn the power off and then carry out all the necessary tests correctly.
You need to isolate each circuit, disconnect them from the MET and then test accordingly
 
FFS ,hit your client over the head with the BBB and tell him either turn the power off for the pitches that dont comply with the reg or some body get else in.simples .
Me i would quote the elec act .
 
Well the panel feeding the sub circuits has Zs of 3.15 and KA of 3.0 but some of the circuits are ok and some are not but there are endless joints underneath the ground so can’t help and glands are ok

Then you've got a serious problem because a Zs of 3.15ohm should give a pfc around 76A at 240V, or a pfc of 3kA would come from a Zs of 0.8ohm.
I'll ask again, what test are you using, high current or anti trip?
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
London
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
High TNS readingssssss
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
60

Advert

Thread statistics

Created
Bradley6969,
Last reply from
sheppertonspark,
Replies
60
Views
5,924

Advert