PAT Tester broken but i can use megger?

Discuss PAT Tester broken but i can use megger? in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
92
Hello guys

my seaward PAT tester has given up the ghost, i have some small PAT jobs coming up and was thinking short term of being able to just use my multi function meter.

R2 test on class 1 equipment using low voltage ohm meter
Insulation resistance testing with leads

Trying to think what other limitations i have by just using my multi function test instrument?
 
If 200 mA is good enough for installation continuity testing, why not not for appliances?
The flex in an appliance would typically take more abuse than fixed wiring embedded in the walls or in a conduit/trunking to be fair. It's not really a like comparison. Although traditionally conduit joints would have been tested at these higher currents.
 
I'd been thinking about making an adapter a bit like that - but with an extra socket for an earth continuity lead and a switch. Idea being that the switch would take care of the different connections needed - so the MFT could stay connected, the extra lead connected to exposed conductive parts for Class I continuity & Class II IR test, and only the switch would need to be moved (plus the mode switch on the MFT).
Otherwise, yes an MFT can be used, it's just a bit of a faff having to reconfigure the leads all the time for the different tests.

How many battery powered PA testers do that ? At my last job (in IT), the boss thought it might be a good idea to get a tester and offer it as a service to customers. My response was that I wasn't going to be the only person "qualified" to do it, and no-one else actually bothered. I borrowed it and used it for my own requirements more than it got used at work (I'd test stuff that came across my desk) ;) Anyway, the spec for it wasn't for much current - only something like 200mA IIRC.
You don't need to be qualified to carry out ISITEE.
 
Technically no you don't need any qualifications. But you do need to be competent, and more importantly, you and your employer need some means of showing that.
In practice, the training (provided as part of the package with the tester) was a 20 minute DVD and a multi-choice test paper. But it does mean I have another "magic piece of paper" ;)
 
I have that magic piece of paper!
Microsoft Publisher, and i can get you one too!
My training actually consisted of a full day, hands- on, plus presentation, plus course manual. It's not exactly rocket science, I know.
The tester I use is a simple Pass/Fail, no bluetooth download, no fancy email reporting, but it can be used battery power or mains.
However, it is only used for landlord testing. Proper electricians like you lot will likely not be impressed!
ISITEE does sound itchy, though...but far preferable to Portable Appliance Testing testing...
but then, why is abbreviation such a long word?
Why doesn't the all-purpose glue stick to the tube?
Why is there only one Monopolies Commission?

Whatever, I just meant that I have no "qualifications", but I am deemed competent, and I actually believe I am competent to do this simple work. However, if anomalies show up, I seek advice, and don't just sticker everything. I do actually test, and do FVI, and as it is an occasional thing for me, I quite enjoy it. If I had to do it every day I would go mad...
 
And that's the thing - being competent. Understanding what the tester is doing and what the results mean.

The problem is when you test something and the tester says Pass, but it hasn't actually tested anything. Figure 8 mains cables come to mind.
 
That's a fair point, DPG!
However, if you have the right adaptors you can test many things...but if you don't know what the tester is doing, you can't be sure...
Recently I tested an office...tons of stuff, but mainly IT.
They had so many extension leads! The Belkin ones failed, time after time...even the non-surge protected ones, but the tester is designed to be that way...I won't bore you with the semantics because you will already know the position...but, oddly, I had never had a fail before on these type of leads. I contacted the tester manufacturer and got an immediate response, which was helpful to me. The client told me to bin them, so I am currently using them at my office-desk! They are absolutely fine!
For me, as an amateur, every day is a learning day. I learn more on here and looking at quality videos than many other so-called learning sources...and there are a couple of guys on here who have given me invaluable assistance on the quiet, so like a new GP, who can't possibly know everything, experience is key.
 
I see where you are going, DPG!
TBH, I ignore F8 leads in the main...they are either working, or short-circuited, which virtually never happens.
Haven't failed an IEC or kettle lead in ages...except for the ones from the big river that are rated 10A and can barely support 3A...and you can spot them right away just by picking them up and handling them.
 
I see where you are going, DPG!
TBH, I ignore F8 leads in the main...they are either working, or short-circuited, which virtually never happens.
Haven't failed an IEC or kettle lead in ages...except for the ones from the big river that are rated 10A and can barely support 3A...and you can spot them right away just by picking them up and handling them.
I actually failed an IEC lead on Monday. I found it not to have earth continuity through it.
 
It happens, for sure, Risteard. Oddly, it's quite rare, but it does happen...which suggests to me that testing them is worthwhile...how else would you know?
However, PA Testing should be outlawed, and ISITEE replace it...
just my opinion...
It should be accorded a proper place in tenancy and office safety.
OK, it's not full-blooded electrics, but it is still important.
 
I failed 8 x IEC320 leads last week. High EB measure prompted a closer look, cut the first one open, inner sheaths were non standard colours, the wire was ridiculously thin I believe copper coated aluminium, so thin I could easily snap sections of it by hand. The other 7 were identical.
 
I failed 8 x IEC320 leads last week. High EB measure prompted a closer look, cut the first one open, inner sheaths were non standard colours, the wire was ridiculously thin I believe copper coated aluminium, so thin I could easily snap sections of it by hand. The other 7 were identical.
Were there any BS numbers on the leads? Surely this should be a requirement for sale in the UK.
 
Still remember when everything from Japan was made from tin (cans) and laughingly called Jap Crap. Then they bought the old assembly line for Austin and using the engine and chassis components designed their Datsun Bluebird. Datsun became Nissan and with Honda,Toyota etc, no ones laughing now. Maybe Chinese will catch on, they are losing “Face” big time!
 
Was a time when fire brigade blamed any device plugged in most of the time.
Video recorders ,
Now we could be moving on from fridges ,to anything with a Chinesium cable .
(did have my doubts about plenty of Phone USB chargers-but have no incoming flex )
 

Reply to PAT Tester broken but i can use megger? in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock