Nov 29, 2019
128
16
93
London
Hi All
Am continuously getting failed EICR'S sent over to quote on remedials for non fire rated downlights. These are lights in question. I see they have exposed conductors so would personally probably code 2 but what would code be for fire rating they are low voltage if that even makes a difference I don't think it does as my understanding of the fire rating it's the degree of protection of a fire from room below spreading into void above and potentially into other apartments.....any clarity appreciated.
First of all. And this is a key point
Fire rated down lights are only required if a fire barrier has been punctured to enable the downlighting. In the vast majority of cases the ceiling is not a fire barrier.
the places you may find a fire barrier are theceiling of an integrated garage or the ceilings between separate apartments where the construction includes a fire barrier.
you’ll spot a fire rated ceiling because it’s made of pink plasterboard or a double thickness plasterboard.
Can’t see for sure but your photo doesn’t show that ceiling as a fire barrier . There’s a general urban myth that fire rated down lights are necessary where there’s a bedroom above a kitchen- that’s tosh.
The only thing I can see wrong in your pic is cable sheath not entering the enclosure. C3.
Thanks Taylor on clarifying on whether the the lights are actually fitted into an actual fire rated ceiling. This actual property is a block of apartments that is a converted warehouse. There is no sign of the lights being extra close to wooden joists but hard to make out if above the actual lights apartments above are separated by wooden flooring. Would this influence your decision on whether the lights should be changed for fire rated ones? Thanks
The point of fire rated down lights is to limit the passage of a fire in a lower floor to the floor above. They are not to allow the download Light to be positioned closer to joists etc or flooring above.
It is the ceiling which is, or isn’t a fire barrier.
Reactions: JohnS888
I would check the void, if it looks like there is fire board there, in good condition. Its a pass. If not and there is a living space above C2 all day. I pass them if there in a loft or flat roof only.
Reactions: JohnS888
Thanks Kellogs it's pretty much how I'm approaching things now
We debated this many times. You have to ask the reason why plasterboard is used. One of the reasons, is to make walls & ceiling’s look nice.
If you decided on a rustic look for your living room and new extension, by exposing your joists and not installing a plasterboard ceiling and leaving the structural elements of the property exposed, I think you would face a hard time getting that passed a Building Control Inspector.
Likewise, if you make a hole in a plasterboard ceiling for services, Building Regs require you to reinstate to its previous condition. You cant leave something worse than it previously was.
Plasterboard also helps in compliance with other Building Regs, not just fire.
Theres a Best Practice Guide from ESF, on this subject, which I haven’t to hand at the mo. Whilst if I recall it doesn’t advise against these old type down lights, it does give some guidance on the matter. I’ll try and find it, when I have time.
Reactions: JohnS888
Thanks Midwest that would be appreciated
https://www.-----------------------.../safer-installations/installing-downlighters/
There‘s a link to their BPG 5.
Thanks Midwest that's an interesting read and hits home quite abit around the safety of incorrect/incorrectly fitted downlights
It might just be me, but single insulated live conductors should not be exposed and are potentially dangerous. And the flex likely won’t be properly strain relieved as well. So C2 from me.
I have never trained as a fire preventative officer, and I don't see that are part of my remit when doing an EICR, I may put it in notes, but if the lights were removed and the originally ceiling rose fitted and holes left in ceiling would it fail an EICR, no it would not, so simply nothing to do with an EICR.
If there is a fire prevention report which picks them up then yes OK.
Eric, your first sentence is a little worrying. You don't see fire prevention as part of your remit when doing an EICR?
In the schedule of Inspections of the EICR form, point 5.13 specifically relates to 'selection and erection of wiring systems to minimize the spread of fire'. See section 527 BS7671.
Deleted. My error.
C3 for the xposed basic insulation.as regards the fire rating, all depends on whether the ceiling is a fire barrier or not.
Reactions: JohnS888
If a tradesman or professional strays out of there remit it can cause all sorts of problems, I had a house buyers report on my house before buying which detailed what had been found on the electrical system.
It said the consumer unit had been up-dated and the old fuse box had been left in place above the ceiling, this was incorrect, the old fuse box was still active, with a hole in the plaster board just big enough to get your hand in to change a fuse.
OK as an electrician I was not worried, but it would be easy for a home buyer to think that home buyers report included an electrical installation condition report as they had reported on the electrical installation condition.
I as an electrician am not qualified to comment on fire prevention, yes I can raise concerns like anyone else that a fire door has been replaced with a not fire resisting door, or there is a whole in the ceiling which also will not resist fire, but plain fact remains if a ceiling rose had replaced the down lights and the down light holes not filled, it would be more dangerous than having down lights in the holes, but would not attract any coding with the EICR, so why should it get a code when less dangerous?
But as an electrician, you should be conversant with Building Regulations, and how electrical installation can have an impact on the regs, and visa versa. This includes fire safety.
We do have a responsibility to make sure we do not aid in the spread of a fire, point 5.13 on the schedule of inspections on the EICR and the entire section 527 of BS7671. What do you make of that section of BS7671 Eric? Genuine question, do you just not think it applies? if so, why not?
London
Can someone please clarify EICR rating of these downlights in terms of fire rating
JohnS888,
HappyHippyDad,