So I've just watched this and the chap explains all the different Earth arrangements used in the UK. He mentions about how in a TN-CS earth system if the neutral was broken just before it came into your house then this would be very dangerous. So I was just wondering if a TT system combined with a CN-CS would be safer.
Or am I missing something he is saying and barking completely up the wrong tree? (which is always quite possible)
What are the chances of the neutral leg being broken between the service head outside your property and your meter without causing some other fault? Pretty much zero.
pme = protective multiple earth. It’s earthed at pretty much every joint; every time the dno do any work on a cable they pme it if not already and put an earth rod in.
you could always bang an earth rod in on a tncs system if it makes you feel better. That’s what other countries do and I think was considered for the 18th?
It was proposed as part of the 18th edition to install supplementary earth electrodes but it never happened.
On a side note it is a DNO requirement to have an electrode to supplement TNC-S systems on metal street furniture subject to certain load and resistance criteria.
Part II of the Electricity Safety, Quality and Continuity Regulations 2002, as amended, which covers protection and earthing, applies to supplies to street lighting installations and other street electrical fixtures.
An earth electrode shall be provided at the end of every service supplying more than one street lamp or road sign.
An earth electrode shall be provided at the source pillar or supply point servicing more than one street lamp or road sign.
There are a few more requirements, such as if the furniture is in insulation, then it needs a rod irrespective etc
Forgot to say, the requirements of G12/4 apply as well
The safety trade off of TN-C-S versus TT is not just about the open PEN conductor risk.
The PEN fault situation is what usually sparks the discussion when looking at hot tubs, etc, outside that may be fed from a TN-C-S supply and where the risk of 80+ volts to true Earth is a whole lot more serious (it also applies in agricultural visitations where animals might be sensitive to far lower voltages that may be present even without a PEN fault as such). In those cases your options are either supplementary earth rods/mesh on to the TN-C-S CPC to keep the step potential down in such a situation, or to go TT and have the local CPC from an earth rod, etc, and basically ignore the TN-C-S derived earth.
But the other side of the risk assessment is the case of a fault to earth within the installation where rapid and certain disconnection is desired. In this case the low Zs from TN-C-S allows you to (usually) meet fault disconnection by means of a fuse or MCB alone, and you are not reliant on an RCD to allow clearing. Given the order of magnitude or more difference in complexity between the two, you can rely on a fuse/MCB (or equivalent OCPD side of RCBO) with greater certainty than the electronics of RCD detection.
While the serious nature of the PEN fault should not be discounted, I suspect installation L-E faults are more common!
But exactly what purpose does an earth electrode (size /length resistance to earth not specified) installed at the base of a street lamp serve? If its not of a very low resistance its of little value on a TNC-S system.
Hi - given that it’s unlikely that DNO N will be broken outside your house I don’t think adding a rod would improve safety. Unfortunately if the N did break we would need a very very good Ra to keep the touch voltages in check.
Having one small rod would make much difference, as above, but if every 2nd house had a 2m rod or similar then it would greatly reduce the risk.
Which is what the 'M' of PME really tries to do anyway, but with the onus on the DNO side.
I notice your concerns about using rcd, s with electronics. Why not turn to rcd, s that don't include electronics? I like the arrangement best where we use the TNC-S, arrangement for ADS but also have an rcd for additional protection. In reality rcd, s are now becoming seen as, required protection, which in reality they are. They are singlehandedly responsible for reducing electrocutions massively in countries that use them as standard
Primarily it ties the local ground to the same potential as the metal furniture, if this was not the case then the ground - and thus the feet of the drunk leaning on the lamp post could raise to some random potential in the event of a fault elsewhere - such as a line-ground fault at the next lamp post - or that one itself so with say 100....230V actually connecting to the ground/drunk's feet, whilst the lamp post itself would be tied to earth at the substation.
Tying the local ground to the same potential as the metalwork in the area prevents this, its one of the principles of equipotential bonding used throughout the 18th.
Rather than of little value, it's of great value
The resistance value to earth isn't unspecified at all; it depends on the load or the unbalance of a 3 phase load - so 500W would be 100ohm, through to 5kW which would be 9ohm - with corresponding values between.
I think you have missed my point. What you state is correct PROVIDING as other posts mention the RA of the rod is very low. If the RA is above 10 ohms (for example), instead of a safety feature, we now have a potential hazard. We simply have another piece of live metalwork. It's not possible to tie any metelwork to to earth potential unless, the contact between them both is virtually resistance free. So to conclude.. if rod is of correct resistance its of great value, if its of high resistance its a potential hazard, adding to the problem rather than alleviating it.
I notice your concerns about using rcd, s with electronics. Why not turn to rcd, s that don't include electronics? I like the arrangement best where we use the TNC-S, arrangement for ADS but also have an rcd for additional protection. In reality rcd, s are now becoming seen as, required protection, which in reality they are. They are single handedly responsible for reducing electrocutions massively in countries that use them as standard
Well you won't get a 30mA RCD in any practical manner without electronics or very delicate mechanical trip mechanisms!
I fully agree that RCDs have massively improved safety against shock and to some degree against fire, so that are very much a good thing.
But I always believe when it comes to safety you don't want a single point of failure. That is why we have double insulation, or an earthed object for ADS and single insulation. In both cases you need two failures for something to be at-risk.
Now you can say that an RCD on TT still needs double fault to be unsafe, the original live-CPC breach and the RCD to fail in detecting the fault current. But as such a fault makes the whole installation's CPC dangerously high in potential for long period you have a greater risk from any lack of supplementary bonding, or from odd external metalwork that is connected to the installation's CPC and touchable (hand railings or fences with lights mounted on them, etc).
If you can disconnect on OCPD or RCD then you need double-faults as well as the (far more likely) initial appliance fault to make things unsafe. As that is impractical with most TT setups I would always prefer a S-type 100mA/300mA RCD incomer and RCBOs for the "30mA additional protection" against shock.
Though I suspect here I am preaching to the choir!
No it isn't.
If there is a fault to earth somewhere; the potential at the ground at the fault would be say 230V (or 6.35kV, 19.05kV or whatever depending on the faulted circuit voltage) and would be zero at the substation earth - all points in between would have various potentials dropping as one gets closer to the substation.
This doesn't matter at any particular point - unless you contact another point a bit further down the route (such as a horse in a field etc) when the potential difference between the points matter.
However if something is directly connected to the earth point at the substation, such as the metalwork of street furniture then it would be very important!
Anyone or anything touching the metal whilst in contact with the ground could receive a considerable voltage (depends on how close to the fault or how close to the substation or nearest earth connection) .
If however there are lots of PME connections to the ground, then a couple of things happen - firstly the local ground is held towards the same as the substations earth (so reduced chance of a potential difference), and the fault current is likely to be larger , so will clear quicker, or in some cases it would actually be detected!
These connections should be as many as possible - not just PME rods in the distribution, but also the bonding to gas/water pipes at each house, to extraneous metalwork etc. (in fact as the move to plastic services increases the need for more distribution rods grows). Tying street furniture with rods does the same thing.
It is also important when you come to more rural areas as the number of distribution services and their PME/extraneous bondings fall.
This would be a cost impact, hence not all take-offs from the distribution system have rods, not all street furniture has rods etc.
The ideal would be for every point possible to have a rod (or rods), as cumulatively this would provide little chance for the local ground to raise potential in the event of a fault, but at a significant financial cost.
In reality there needs to be sufficient bonding to local ground everywhere to provide a safe potential in the event of a fault etc. Any further would be added cost, yet not provide anything.
Take any circuit in a home, if it has sufficient CPC to clear the fault in 0.4s should we all add another separate CPC to make sure?
On street furniture I was under the impression that the electrode on a TNC-S was there in case of a vehicle hitting the equipment and potential damage to the supply cable, this is also in additional to tying the equipment down to local earth potential.
I think this point has been raised before, and I think I'm right in saying they are some 300 injuries per annum, from a broken PEN conductor (source HSE, though I haven't a link for that.....at the moment).
I guess different networks will have different policies. WPD guys when replacing a transformer the other day said the only way you could guarantee a tns connection is if you had your own transformer on site.
The last couple of 'TN-S' supplies I've tested have had Ze of 0.3 or so, suggesting that they are likely TNC-S in reality. I've also heard others say that large parts of the country are effectively that, regardless of the service head.
"tying the local ground to the same potential as the metelwork.." I, may be missing what you are getting at here, but to create an equiopotential bond between the metelwork and the ground would require a rod with virtually zero resistance?
We create equipotential bonds in the home by eliminating the resistance between two conductive services. No resistance equals no volt drop.
How in practice would you "tie the equipment down to local earth potential"?
No, you just need enough of a ground rod or mat that it pulls the local Earth up to a similar potential.
It is very hard to pull the PME down to close to true 0V, that needs a very low rod Ra, but much easier to pull up the local surroundings so the touch/step potentials are tolerable. While that may not stop equipment being damaged by 300V+ AC supply, but it might stop someone nearby from getting a life-threatening shock from any extraneous parts.
But if we take a rod in a TT installation. Under fault conditions the top of the rod could well be at near mains potential. And for argument sake, 2 to 3 feet further out may be at zero potential. I am trying to grasp how that could constitute an "equiopotential zone"?
That is a very short & poor rod!
Yes it is not a simple thing to do, but having something down in the tens of ohms range probably implies a reasonable region of equipotential from it.
Agreed. But its more the principle I am looking at. To create an equipotential zone in a home we use bonding conductors that would need to be below 0.5 ohms. What sort of resistance then would the rods have that are sunk at the base of a street lamp require in order to create a similar effect?. Or is my reasoning off the wall here?
0.5 ohm is very low - but the sort of thing for keeping N down to a few volts.
Realistically if you have local rods in the tens of ohms I would expect to see local touch potentials kept down below 50V or so. However, this is Sunday and I have had more wine than is reasonable to attempt any computation of this!
First and foremost you enjoy your Sunday (and your wine!). The main problem I have with Sunday is how quickly it becomes Monday. Will get back to this another time.
Well you seem to be working your way across the continent very fluidly!
Yes, doing my bit!
I have some decent Spanish wine as well, and there is even good English wine from Nyetimber if you like the Champaign style. Going further north is a struggle for good grape growing weather, but locally the is Cairn O'Mohr who make good wine from fruits.
Still scratching my head on this.
So the myenergi device, has a voltage monitoring device and this ‘alternative device’ (an RCD that monitors the current flowing to earth)?
So looking at the later, a person may endure around a 30mA shock before the device disconnects, and the device still needs a reference point with Earth. Doesn’t this reference point still need to be 2-10m from other rods or buried metallic objects?
Bearing in mind ventricular fibrillation can occur at 30mA. Doesn’t appear sorted to me.
It is basically an RCD that looks at CPC current as well. So yes they can get up to 30mA before it trips but that is the same as any other RCD for "additional protection". Not fun, but in most cases not fatal.
I don't think it needs any Earth reference which is the main selling point.
Basically if the volts are out of range it opens L, N and E (probably a normally-open contactor, which would deal with an close-by open N+E fault that would rob a protection circuit of its operating power supply), and if it detects a 30mA leakage current on CPC (and presumably L&N for normal RCD protection?) it also disconnects.
There, s more than one head been scratched at the moment. I am genuinely perplexed at a number of the comments in Julie's post and would be very happy to be corrected
First, the "equippotential zone" created by the rod which "ties the local ground to the same potential as the metelwork".
Equipotential means "same potential". That would require zero "touch voltage" at the rod. Zero "touch voltage" at the rod would require a rod with zero resistance.
Second. Regarding the drunk with his feet on the earth who is simultaneously touching the earthed metelwork. Is, nt the earth he is standing on also tied to earth at the substation,? similar to the the earthed metelwork he is touching?
Third :If there was a line to earth fault at the pole further up. In a tncs system the voltage at the rod will never be more than the voltage across the neutral that's, its connected in parallel with. So let's say 50 volt approx. However that rod still has a contact resistance with the ground of dozens of ohms. And as with any rod there will be step voltage that gradually reduces. Where then does the voltage come from that poses such a danger at the feet of the drunkard.?
Hope there is at least a little sense in what's written above.
My interpretation of what Julie was suggesting is that in a perfect stand-alone circuit it's exactly that - same as in any circuit load - the pd varies on the circuit dependant on where you measure it versus the load. So if there was only one energy source on the literal world and one drunk and one lamp post it becomes some maths to work out that A to B to C where B is a factor of distance/resistance/voltage, diminishing from A = 230v (say) to C = 0v. But by having another conductor route from A > C in the form of a cable we create a parallel path so now B is B/2 (or whatever resistances are involved). Now imagine that we have multiple sources of energy and multiple parallel paths and rapidly we end up with B/∞ which clearly is 'not a lot'. This is what happens when we 'ground' multiple times. If we all of us walked around in our daily lives with stupidly long fly leads attaching our bodies to the neutral points on the nearest sub station we wouldn't need cpc's or bonding to keep us safe - but as that's as ridiculous as it is impractical we instead have as many points around us at anyone time which ARE linked back, and we use technology such as RCD's to account for the stage in-between us and that nearest point.
Pedants..... yes, that's a very simplistic view!
No argue with Julie's reasoning about regarding about role improved earthing and bonding in general play.
But it's the point about creating an equiopotential zone between the metelwork and the local ground through the sinking of an earth rod at the base of the lamp.
Let's take a practical example. In the link from "pretty mouth" on this thread "my energy" state that to keep the touch voltage at 70 volts at an earth electrode during a fault at their EV socket would require a rod with a resistance of 2.5 ohms, which they regard as been impractical to achieve. That is thus 70 volts potential difference from the top of the rod measured measured against the ground 2 to 3 feet outwards from the rod.Does that qualify as an "equiopotential zone"?
What then qualifies Julie, s example as an equiopotential zone?
My brain hurts now. An EQPZ is simply an 'area' (as defined by the duration of a low enough resistance) where no pd exists between two points - so going back to basics we bond the neutral of our energy to actual earth, our water pipe also to it, gas etc etc, such that if I happen to grab onto the kitchen sink at the same time as brushing against the toaster (whatever...) then because they are both part of the same eqpz then no volts can exist between the two conductors. Theoretically, if you had long arms and grabbed the neighbours toaster then you could take a belt if it was from a different energy source.
Can totally relate to the "hurting brain" bit. But your point is the same conventional electrical principal we have all been taught. An EQPZ means no PD between 2 points. And that is not achievable with a standard rod (or even several)
Bucks
TN-CS Combined With TT Question
OnlQQker,
LastManOnline,